What is the procedure for calibrating the flowserve logix500 si series ip positioner?

What is the procedure for calibrating the flowserve logix500 si series ip positioner?

To calibrate the Flowserve Logix 500si series digital positioner:

  1. Press the QUICK-CAL button to easily and quickly calibrate the positioner on all actuators without physical stroke stops.
  2. The calibration process will be completed when the lights return to a sequence that starts with a green light.
  3. Commissioning is performed by simply setting a few switches and pressing the QUICK-CAL button. The Direct User Interface provides local access to positioner control without requiring multi-level menus, a handheld communicator or laptop computer.
  4. Fast calibration and setup can be made by simply pressing the Quick-Cal button. Interchangeable components (such as circuit board, piezo drivers, etc.) allow for easy maintenance.

The Flowserve Logix 500 SI Series I/P positioner requires multiple steps to calibrate. The following is a generic process outline to help you through it:

Tools and Equipment Needed:

  • Flowserve Logix 500 SI Series I/P positioner
  • Handheld communicator or calibration device (such as HART communicator)
  • Power supply (if necessary)
  • Appropriate documentation (e.g., the user manual for the specific model)

Calibration Procedure:

  1. Safety Precautions:
  • Ensure that the valve and actuator system is depressurized and de-energized before starting.
  • Follow all relevant safety guidelines and lockout/tagout procedures.
  1. Setup:
  • Connect the handheld communicator to the positioner. If using a HART communicator, connect it to the current loop.
  • Ensure that the positioner is properly installed on the actuator and that the air supply is connected and regulated to the correct pressure.
  1. Power On:
  • Power on the positioner and the handheld communicator. Wait for the devices to initialize.
  1. Enter Calibration Mode:
  • Use the communicator to navigate to the calibration mode on the positioner. This might involve accessing a specific menu or pressing a combination of buttons.
  1. Zero Calibration:
  • Set the input signal to 4 mA (or the lower range value, typically corresponding to 0% position).
  • Ensure that the valve is in the fully closed position.
  • Initiate the zero calibration process via the communicator. The positioner will adjust itself to recognize the fully closed position as 0%.
  1. Span Calibration:
  • Set the input signal to 20 mA (or the upper range value, typically corresponding to 100% position).
  • Ensure that the valve is in the fully open position.
  • Initiate the span calibration process via the communicator. The positioner will adjust itself to recognize the fully open position as 100%.
  1. Intermediate Points:
  • Some positioners may require calibration at intermediate points (e.g., 25%, 50%, 75%). Follow the prompts on the communicator to set these points if necessary.
  1. Verification:
  • After calibration, verify that the positioner correctly responds to the full range of input signals (e.g., 4 mA to 20 mA) and that the valve moves accurately to the corresponding positions.
  • Look for any alarms or error messages on the positioner or communicator display. Keep and Leave:.
  1. Save and Exit:
  • Save the calibration settings if prompted by the communicator.
  • Exit the calibration mode and return the positioner to normal operating mode.
  1. Documentation:
  • Record the calibration results and any observations for future reference.

Troubleshooting:

  • If the positioner does not respond correctly during calibration, check the air supply, wiring, and connections.
  • Refer to the user manual for specific troubleshooting steps related to your model.

Always refer to the specific user manual for the Flowserve Logix 500 SI Series I/P positioner you are using, as there may be model-specific steps or variations in the procedure.