What is the Normally Permitted Motor Ratings as per DEWA?
Motor ratings are regulated by the Dubai Electricity and Water Authority (DEWA) to minimize starting current, voltage drop and system disturbance. The typically permissible motor ratings (without special approval or additional starting procedures) are shown below:
Normally Permitted Motor Ratings (LV – 415 V, 3-Phase)
1). Direct-On-Line (DOL) Starter
Motor Rating Permission Status
Up to 7.5 kW (10 HP) Normally permitted
> 7.5 kW Not permitted with DOL (approval required)
Note: DOL starting draws 6-7 times the rated current resulting in voltage drops that are inappropriate for heavier motors.
2). Star–Delta Starter
7.5 kW to 30 kW (10–40 HP) Normally permitted
> 30 kW Requires DEWA approval / justification
3). Soft Starter
Up to 75 kW Generally permitted
> 75 kW Subject to DEWA study & approval
4). Variable Frequency Drive (VFD / VSD)
Up to 150 kW Normally permitted
> 150 kW DEWA load study & approval required
Note: VFDs are popular because they require less starting current and provide regulated acceleration.