what is STUB protection in transmission system and switchyard area?

what is STUB protection in transmission system and switchyard area?

STUB protection is an enhanced form of Overcurrent protector and is used significantly in transmission system networks especially, the OAHS which is the one and a half breaker scheme.
Specifically, it is intended to shield areas of the power system for which regular distance protection is not effective when the line isolators are switched off.
STUB protection is necessary when the input is disconnected by the opening of the line isolator, which cannot send required voltage and current to the distance protection.
In such cases the region between the circuit breakers and the open isolator can be prone to the faults and hence the STUB protection is provided as one form of back up protection.
The fact is the functioning of STUB protection is based on the status of the line isolator.
When the isolator is open, STUB protection system is operative, the current is covered by the distance relay.
The protection is normally set to snap if the current of fault is above a certain level, often above the full load of current on the line.
It allows the equipment to operate normally without the flowing current tripping and yet provides quick fault clearance when the isolator breaker is open.
Here, one can note that STUB protection is only activated when the isolator of the line is open.
The current threshold is chosen to be higher than the full load current so as to prevent the circuit breaker from tripping during normal operations.
The time delay of tripping is most preferably set to zero or less than the Zone-2 time delay for tripping the connected lines to counter faults.