What are the tests conducted on a circuit breaker?

As such the IEC standards governing Circuitbreaker / Isolators is IEC 62271-1-2007

the following are the tests conducted on a Circuit Breaker :

  1. Power Frequency voltage withstand test

  2. Lightning Impulse Withstand test

  3. Switching Impulse voltage withstand test

  4. Visible corona test

  5. Corona Inception/extinction test

  6. RIV test

Testing a circuit breaker is crucial to ensure its reliability, safety, and proper functioning. Here are some of the common tests conducted on circuit breakers:

  1. Visual and Mechanical Inspection:
  • Inspect for physical damage.
  • Check for proper mounting and alignment.
  • Ensure all connections are tight and secure.
  • Verify the operation of mechanical components.
  1. Insulation Resistance Test:
  • Measure the resistance of the insulation between the breaker’s current-carrying parts and the frame.
  • Typically conducted using a megohmmeter.
  1. Contact Resistance Test:
  • Measure the resistance of the closed contacts.
  • Performed using a micro-ohmmeter or ducter.
  1. Dielectric Test (Hi-Pot Test):
  • Apply a high voltage to the breaker to ensure that the insulation can withstand the operating voltage.
  • Verify insulation strength and detect weak points.
  1. Operational or Functional Test:
  • Manually operate the breaker to ensure it opens and closes properly.
  • Check the tripping mechanism for proper operation.
  1. Trip Timing Test:
  • Measure the time it takes for the breaker to trip under various fault conditions.
  • Conducted using a secondary current injection test set.
  1. Primary Injection Test:
  • Inject a high current through the breaker’s primary circuit to test the overall tripping operation and response.
  • Simulates actual fault conditions.
  1. Secondary Injection Test:
  • Inject a current into the secondary circuit of the protective relays to verify the relay settings and operation.
  • Ensures the relay will trip the breaker under fault conditions.
  1. Thermal Imaging:
  • Use an infrared camera to detect hot spots that indicate poor connections or overloading.
  1. Contact Timing Test:
  • Measure the time between the initiation of the trip command and the actual contact separation.
  • Ensure synchronization of all phases.
  1. Overload Trip Test:
  • Simulate an overload condition to verify the breaker’s ability to trip after a specified delay.
  1. Short Circuit Trip Test:
  • Simulate a short circuit condition to verify the breaker’s instantaneous trip capability.
  1. Interruption Capacity Test:
  • Test the breaker’s ability to interrupt a high-current fault condition.
  • Ensures it can handle and clear fault conditions without damage.
  1. Calibration Test:
  • Verify that the breaker’s trip settings are accurate and within specifications.
  • Adjust settings if necessary.
  1. Endurance Test:
  • Repeatedly operate the breaker to simulate long-term use and ensure it can withstand mechanical wear.
  1. Ground Fault Test:
  • Verify the breaker’s ability to detect and trip on ground faults.

These tests are essential to ensure that circuit breakers perform reliably under various conditions and provide necessary protection to electrical systems.