What are the key rooms commonly located inside a substation control building?

What are the key rooms commonly located inside a substation control building?

Reference Image Provided by the Respondent

The Substation Control Building houses the equipment & facilities required for monitoring, protection, control, communication and operation of the electrical substation.

The exact room arrangement depends on the voltage level and substation size, but the following rooms are commonly found:

  • Control Room
  • Protection Relay Room
  • Battery Room
  • Battery Charger Room
  • Communication/SCADA Room
  • UPS Room
  • Metering Room
  • Cable Basement/Cable Gallery

These rooms form the backbone of substation protection, control, monitoring, communication and reliable operation.

1. Control Room

Main operating room of the substation.

Contains:

  • SCADA workstations
  • HMI systems
  • Annunciator panels
  • Control desks
  • Mimic panels

Used for monitoring and controlling all substation equipment.

2. Protection Relay Room

Houses protection relay panels.

Contains:

  • Distance relays
  • Differential relays
  • Overcurrent relays
  • Transformer protection relays
  • Bay control units

3. Battery Room

Contains station batteries.

Common battery systems:

  • 48 V DC
  • 110 V DC
  • 220 V DC

Provides backup power for:

  • Protection systems
  • Circuit breakers
  • Emergency lighting
  • SCADA equipment

4. Battery Charger Room

Contains battery chargers and DC distribution boards.

Maintains battery charging and DC supply continuity.

5. Communication Room

Houses communication equipment which includes:

  • RTU panels
  • Communication gateways
  • Fiber optic equipment
  • Ethernet switches
  • Teleprotection equipment
  • Modems and routers

6. SCADA / Automation Room

Dedicated room for automation systems that contains

  • SCADA servers
  • Data historians
  • Engineering workstations
  • Network servers

7. Metering Room

Contains energy metering equipment that includes:

  • ABT meters
  • Revenue meters
  • Energy monitoring systems
  • Meter test facilities

8. AC Distribution Room

Houses ACDB panels which supplies:

  • Lighting
  • HVAC systems
  • Socket outlets
  • Auxiliary loads

9. DC Distribution Room

DC Distribution Room contains

  • DC distribution boards
  • DC feeder panels
  • Protection and control supply circuits

10. PLC / RTU Room

PLC / RTU Room used in modern automated substations that contains

  • PLC panels
  • RTUs
  • I/O modules
  • Automation controllers

11. Engineering / Maintenance Room

Used by engineers and technicians which stores:

  • Relay testing equipment
  • Laptops
  • Drawings
  • Maintenance records

12. Cable Basement / Cable Gallery

Located below the control building.

Used for routing:

  • Control cables
  • Protection cables
  • Fiber optic cables
  • Power cables

13. Store Room / Spare Parts Room

Stores:

  • Relays
  • Fuses
  • Lamps
  • MCBs
  • Circuit breaker spares
  • Testing accessories

14. UPS Room

Contains UPS systems.

  • Provides uninterrupted power to
  • SCADA
  • Communication systems
  • Computers
  • Critical control equipment

15. HVAC / Utility Room

Houses:

  • Air-conditioning units
  • Ventilation systems
  • Fire suppression controls

16. Fire Protection Room

Contains:

  • Fire alarm panels
  • Fire suppression controls
  • Smoke detection systems

17. Operator Office / Meeting Room

Administrative area for:

  • Shift operators
  • Engineers
  • Operational meetings

Typical Layout of a Modern 110 kV / 33 kV / 11 kV Control Building

Control Room Relay Room SCADA Room
Communication Room Metering Room PLC / RTU Room
Battery Room Battery Charger Room UPS Room
Store Room Maintenance Room HVAC Room
Cable Basement / Cable Gallery Below Building