1) OC / OCF – Over Current Fault
Causes:
-
Mechanical overload / jam
-
Short circuit / insulation failure
-
Sudden load pickup
-
Very low acceleration time
Checks:
-
Measure motor current vs FLA
-
Megger motor + cable (IR ≥ 1 MΩ/kV)
-
Inspect coupling, bearings, gearbox
-
Increase accel time
Protection ref: ANSI 50 / 51, VFD I²t model
Tip: Always enter correct motor rated current in parameters.
2) OV – Over Voltage Fault
Causes:
-
Regenerative load (crane, lift, downhill conveyor)
-
Fast deceleration
-
High incoming voltage
Checks:
-
Monitor DC bus (typically trips at ~1.35 x Vdc rated)
-
Increase decel time
-
Install braking resistor / chopper
Protection ref: ANSI 59
Tip: Regeneration energy must be dissipated, not blocked.
3) UV – Under Voltage Fault
Causes:
-
Weak grid / transformer
-
Loose MCC terminals
-
Phase drop
Checks:
-
Measure line voltage under load
-
Tighten MCCB/contactor
-
Check phase balance (<2–3%)
Protection ref: ANSI 27
Tip: UV = upstream electrical problem in 80% cases.
4) OL – Overload Fault
Causes:
-
Continuous mechanical overload
-
Wrong motor sizing
-
Wrong cooling class
Checks:
-
Verify kW matching (motor vs VFD)
-
Inspect driven equipment
-
Check thermal class (Class F/H)
Protection ref: ANSI 49
Tip: Mechanical problem first, electrical second.
5) OH / OT – Over Temperature Fault
Causes:
-
Fan failure
-
Dust & clogged heatsink
-
Poor panel ventilation
Checks:
-
Clean heatsinks
-
Verify fan RPM
-
Maintain panel temp < 40°C
Tip: Every 10°C rise = ~50% reduction in VFD life.
Professional troubleshooting sequence (always follow):
-
Note exact fault code
-
Measure supply voltage & phase balance
-
Measure motor current
-
Megger motor & cables
-
Verify parameters
-
Inspect mechanical load
-
Check cooling system