Transformer Winding Resistance Test

Transformer Winding Resistance Test

Reliable transformer operation begins with verifying the health of its windings. The Winding Resistance Test plays a key role in ensuring electrical and mechanical integrity before energization and during periodic maintenance.

This test includes applying a controlled DC current to the transformer windings and measuring the voltage drop.

Consistent and accurate winding resistance values ensure efficient current flow, reduced losses, and reliable long term performance.

This test is a foundation step in transformer reliability and is performed during factory acceptance, commissioning, and routine diagnosis.

Required Equipment

Digital resistance meter or DC winding resistance tester

Test leads with Kelvin (four wire) connection Temperature measuring device (thermometer or RTD input)

Safety PPE

Precautions Before Testing:

Transformer must be fully de energized and isolated

Discharge all windings to remove residual magnetism

Ensure no trapped charge in bushings

Record ambient and oil temperature

Test Procedure

Step 1: Verify Test Setup

Identify transformer terminals for HV winding and LV winding.

Ensure correct test range on the resistance tester.

Step 2: Connect Test Leads

Use Kelvin four terminal method

(2 leads for current injection, 2 for voltage sensing).

Connection layout

Primary side: Connect to bushings (A, B, C or H1, H2, H3)

Secondary side: connect (a, b, c or X1, X2, X3)

Step 3: Stabilize and Apply DC Current

Start the tester and apply a controlled DC current.

Allow reading to stabilize because inductance delays steady state.

For large transformers stabilization may take several minutes.

Step 4: Measure and Record Readings

Record resistance values for each phase and tap.

Step 5: Repeat for Other Tap Positions For OLTC (On Load Tap Changer) transformers Record values for every tap position to detect contact resistance issues.

Step 6: Correct Readings for Temperature Transformer resistance varies with temperature. Standard temperature correction formula R2 = R₁x (T2+234.5) (T₁ + 234.5) Where

R₁ = measured resistance

T₁ = measured temperature

T₂ = reference temperature (usually 20°C)

Step 7: Compare With Reference Data Compare values with previous records and manufacturer tolerances.

Normal variation range between phases should be small.

Large deviations indicate potential issues such as Loose joints, Damaged windings, Tap changer contact faults.

Step 8: Discharge the Winding

After the test, allow winding to discharge until voltage reaches zero.

Never disconnect leads immediately because inductive windings store energy.

Acceptance Criteria

Phase resistance imbalance must be within acceptable tolerance.

No abnormal increase vs previous test history.

Smooth resistance variation across tap changer positions.