Transformer Short Circuit Calculation: Full Load, Impedance & Motor Contribution

Transformer Short Circuit Calculation: Full Load, Impedance & Motor Contribution

CALCULATOR

* Transformer Short Circuit Current Calculation

1). Full Load Current

The current generated by an electrical device (such as a motor or transformer) when functioning at full capacity.

IF.L. = TXkVA × 1000√3 × VL−L (A)

2). Transformer Impedance

The internal resistance provided by a transformer to the flow of electrical power, which restricts short circuit current.

Z = VL−L2TXkVA × 1000 × %Z100 × 90% (Ω)

3). Short Circuit Current

The extremely high current that flows when a fault forms as a result of a direct connection between phases (or) phase-earth.

IS.C. = VL−L√3 × Z × 1000 (kA)

4). Motor Contributed Short Circuit Current

Running motors supply greater fault current during a short circuit because of the mechanical energy they store.

IS.C.Motor = 4 × IF.L.1000 (kA)

5). Total Symmetrical Short Circuit Current

The overall fault current at a given point in the system including contributions from transformers, generators & motors providing the waveform is balanced.

IS.C.Total = IS.C. + IS.C.Motor (kA)

6). Multiplier

A factor used to alter or scale current values while calculating, coordinating, or establishing protection devices.

M = IS.C. /IF.L