TRANSFORMER RATING CALCULATION (kVA)

Transformer rating is generally expressed in kVA (kilovolt-amperes), not kW. The kVA rating indicates the apparent power that a transformer can supply within its voltage, current, temperature-rise, and insulation limits.

CALCULATOR

Transformer KVA Calculator based on load

Transformer Rating (kVA) = Voltage x Current / 1000

SINGLE-PHASE TRANSFORMER

kVA = (V x I) / 1000

THREE-PHASE TRANSFORMER

kVA = (√3 x V x I) / 1000

WHERE

V = Voltage in volts

I = Current in amperes

√3 = 1.732

SINGLE-PHASE EXAMPLE

Voltage = 230 V

Current = 43.48 A

kVA = (230 × 43.48) / 1000

kVA ≈ 10 kVA

Transformer rating = 10 kVA

THREE-PHASE EXAMPLE

Line voltage = 415 V

Line current = 13.92 A

kVA = (1.732 x 415 x 13.92) / 1000

kVA ≈ 10 kVA

Transformer rating = 10 kVA

LOAD-BASED CALCULATION

If the load is given in kW:

Required kVA = Load (kW) / Power Factor

Example:

Load = 80 kW

Power factor = 0.8

Required kVA = 80 / 0.8

Required kVA = 100 kVA

With allowance for future expansion, inrush current, harmonics, ambient conditions, and continuous loading, the selected standard transformer rating may need to be higher than the calculated minimum.

IMPORTANT SELECTION FACTORS

• Connected and maximum demand load

• Power factor

• Future load growth

• Motor starting current

• Ambient temperature

• Harmonic loads

• Cooling method

• Voltage ratio and frequency

• Applicable standards and manufacturer recommendations

IMPORTANT NOTE

The final transformer rating must be selected by a qualified electrical designer after checking demand load, diversity, voltage regulation, protection, short-circuit level, and installation conditions.