Below procedure is carried out with SCOPE RECORDER instead of CRO
- Use spare card for testing of scan time for C300 controller.
- Check CEE scan rate which would be configured for 50ms
- Create a new CM and assign execution time to be of 50ms. It is always configured in default(1sec)
- Change execution phase to 0
- Change scan rate of respective DI and DO modules to IOM Priority.
- Build the respective logic and download. i.e. DI channel, flag and DO channel block etc.
- Connect SCOPE RECORDER Out 1 Probe to DI channel 1 i.e. connect its Red terminal to pin 2 of DI and black terminal to reference. Normally we get 24vdc on pin 1 of DI. Short pin1 and pin2. You will get pulse on SCOPE RECORDER and hence DI channel becomes HIGH on CM.
- Connect SCOPE RECORDER Out 2 Probe to DO channel 1 i.e. connect it to terminal 1 and terminal 2 with red being connected to 1 and black to 2.
- Set intervals of waveforms in msec.
- Check whether both waveforms are appearing in SCOPE RECORDER.
- Logic gets executed and waveforms can be seen in SCOPE RECORDER