Ring Main Unit (RMU) Testing
Before starting into operation, an 11kV (or) 33kV Ring Main Unit (RMU) must go through a series of tests to assure its safety, reliability, and performance. These tests can be classified as
• Factory Acceptance Tests (FAT),
• Site Acceptance Tests (SAT), &
• Routine Maintenance Tests.
Factory Acceptance Test (FAT)
These are done in the manufacturer’s facilities before shipment.
• Dielectric Tests: Power Frequency Withstand Test (applied voltage) - Impulse Voltage Test (insulation strength)
• Primary and Secondary Injection Tests: Verify CT ratios & protection relay operation.
• High Voltage Test: High voltage test ensures RMU can withstand rated voltage without breakdown.
• Partial discharge test: Partial discharge test detects insulation problems.
• Gas Insulation Leakage Test: Ensures SF6 (or) vacuum insulation meets approved standards.
• Contact Resistance Test: Determines switching contact resistance.
• Mechanical Operation Test: Ensures smooth functioning of circuit breakers, isolators, & earthing switches.
• Temperature Rise Test: Assesses heating effects at rated current.
• Protection Relay Testing: Ensures proper operation of protection functions such as overcurrent and earth fault.
• IP Rating Test: Ensures dust and water ingress protection (IP65 or higher).
Site Acceptance Tests (SAT)
Site Acceptance Tests (SAT) are performed after RMU installation and before commissioning.
• Insulation Resistance Test: Uses a megger to ensure insulation integrity.
• Circuit Breaker Timing Test: Tests the opening and closing times of the load break switch & circuit breaker.
• SF6 Gas Pressure Test: Ensures proper gas pressure levels (if SF6 insulated).
• Earthing and Continuity Tests: Earthing and continuity tests ensure proper grounding of RMU.
• Functional and Interlocking Tests: Functional and interlocking tests ensure proper operation of all interlocks.
• Load and No-Load Operation Tests: Load and no-load operation tests confirm smooth switching under load and no-load conditions.
• Voltage Transformer and Current Transformer Ratio tests: Ensure proper transformer ratios for metering and protection.
• Check Secondary Wiring & Protection Relay Configuration: Used to ensure proper relay connections and settings.
Routine and Periodic Maintenance Tests
These tests are carried out on a regular basis to verify that reliability remains consistent.
• Gas pressure and leakage testing for SF6-insulated RMUs
• Thermographic scan for hotspot detection
• Contact resistance measurement
• Tests include dielectric strength, breaker timing, and insulation resistance.
• Protection Relay Testing and Calibration
Conclusion
These tests guarantee that RMUs function safely, efficiently, & reliably within the power distribution network. Proper testing reduces the likelihood of malfunctions, power outages, & equipment failures.