Mag Flowmeter Showing Zero Flow – What Do You Check First?

Mag Flowmeter Showing Zero Flow – What Do You Check First?

An electromagnetic flowmeter on a cooling water pipeline suddenly indicates zero flow, even though the pump is running and the process is clearly flowing. Power supply, diagnostics, pipe fullness, and fluid conductivity are all confirmed normal.

What is the FIRST thing you personally check in the field in this situation?

This is a typical problem with a mag flowmeter, and since power, diagnostics, pipe fullness, and conductivity are all fine, we are definitely past the “basic checks.”

The first item I check in the field is: Grounding or Earthing the Mag Flowmeter

If the measuring circuit doesn’t have a good reference ground, a magnetic flowmeter will display zero flow even if everything else is excellent.

Why grounding is the first step

An electromagnetic flowmeter measures flow by using a very small voltage that is created when a conductive fluid cuts through a magnetic field. This signal is in microvolts, which means that

Any missing or bad grounding

Floating pieces of pipe

Rings that aren’t grounded properly

Earth continuity is broken

will make the transmitter lose its reference and bring the signal down to zero, even though water is plainly flowing.

What I check on site in this order

Continuity of the grounding cable from the flowmeter body to the plant earth

Presence of grounding rings (particularly on lined pipes made of rubber, PTFE, or epoxy)

Jumpers that connect across insulating flanges

Corrosion or loose terminals on the grounding lug

Check the resistance to earth (it should be very low, usually less than 1 ohm).

This problem happens a lot in cooling water systems because: Pipes are commonly lined with rubber.

Temporary bypass spools interrupt the connection between the ground and the power source.

Teams that do maintenance take off bonding straps and forget to put them back on.

Why not start with the electrodes or the signal wiring?

Usually, noisy or unstable readings are caused by electrode coating, polarity reversal, or cable problems, not a clean, solid zero with good diagnostics. On the other side, a grounding problem makes a perfectly “healthy” transmitter show no flow.

If a mag flowmeter suddenly indicates 0% flow while the process is going on and all the tests are fine, check the grounding before doing anything further.

That’s where the problem is hiding nine times out of ten.

1 Like
  1. Power Supply Issues
  2. Unstable power supply or power failure: This may cause the display to malfunction. Check that power connections are secure and ensure a stable, reliable power source.
  3. Blown fuse: Inspect the power fuse for integrity; replace immediately if blown.
  4. Inadequate supply voltage: Verify that the supply voltage falls within the device’s specified range; adjust or replace the power source if insufficient. II. Sensor Malfunctions
  5. Sensor damage: Issues such as electrode contamination, breakage, or internal component failure directly impact measurement signal transmission and display. Inspect the sensor for integrity and replace promptly if damaged.
  6. Sensor zero drift: Conduct regular zero calibration and adjustment to minimise the effect of zero drift on measurements. III. Changes in Fluid Conditions
  7. Fluid Instability Factors (e.g., Bubbles, Vortexes): These may compromise measurement signal stability. Inspect fluid flow conditions to ensure stable, full-pipe flow.
  8. Contaminants in Fluid: Implement fluid filtration to minimise the impact of impurities on measurement values. IV. Pipeline Installation Issues
  9. Improper pipeline installation position: Excessive vertical or inclination angles may prevent the sensor from accurately detecting fluid flow. Adjust the sensor’s mounting position to ensure vertical or inclination angles remain within permissible limits.
  10. Insufficient liquid filling: Verify that the pipeline is fully filled with liquid. If not, implement measures to ensure complete filling. V. Cable and Connection Issues
  11. Signal cable damage or breakage: Inspect the signal cable for integrity. Replace immediately if damaged.
  12. Incorrect cable connection: Verify cable connections are secure. Reconnect any loose connections. VI. Other Factors
  13. Damaged converter components: If converter component failure is suspected, replace the faulty part.
  14. Electromagnetic interference: Install electromagnetic shielding around the sensor to minimise interference effects on measurements. When troubleshooting electromagnetic flowmeter malfunctions where flow readings are absent, systematically examine and eliminate potential causes to ensure proper operation. Should the issue persist, consult professional maintenance personnel or the flowmeter equipment supplier.