How to select the correct Potential Transformer rating for Protection and Metering?

A [url= Potential Transformer (PT) Testing Procedure][color=#1E00A3] Potential Transformer (PT) [/color][/url] steps down high system voltage to a safe, standardized low voltage for:

1). Metering (energy, voltage, power)

2). Protection relays

3). Control and indication circuits

It must:

• Maintain voltage accuracy

• Withstand system overvoltages

• Supply required VA burden without excessive error

PT Primary Voltage Selection

a) Based on System Voltage

Potential Transformer (PT) primary rating must match system [url= Line To Phase Voltage Calculator][color=#1E00A3] phase voltage. [/color][/url]

Voltage. PT Primary (Star)

11 KV 11 / √3 = 6.35kV

33 KV 33 / √3 = 19.05kV

66 kV 66 / √3 = 38.1kV

132 kV 132 / √3 = 76.2kV

Star-connected PTs are most common in most of substations.

PT Secondary Voltage Selection

Standard secondary voltages:

1). 110 V (most common)

2). 110 / √3 = 63.5 V (phase voltage)

3). 100 V (some standards)

Modern relays are designed for 110 V seconds.

PT Burden Calculation (IMP)

Burden is the total VA load connected to the Potential Transformer (PT) secondary.

It includes:

1). Protection relays

2). Metering devices

3). Indicating instruments

4). Cable losses

Device: Burden (VA)

Numerical protection [url= Phase Failure Relay (Voltage Monitoring Relay): Complete Guide for Three-Phase Motor Protection][color=#1E00A3] relay: [/color][/url] 10VA

Energy meter: 5 VA

Voltmeter: 2 VA

Selector switch + wiring: 3 VA

Total Actual Burden = 10 + 5 + 2 + 3 = 20 VA

Apply Engineering Margin

PT should never be operated at full rated burden.

Recommended margin:

20–30%

Required VA = 20 x 1.25 = 25VA

Selection of PT VA Rating

PTs are manufactured in standard VA ratings:

25 VA

50 VA

100 VA

200 VA

Always select the next higher standard rating.

Selected PT Rating = 50 VA

Accuracy Class Selection

Accuracy class defines maximum permissible voltage error.

Metering PT

Used for billing & measurement:

  • Class 0.2
  • Class 0.5

Lower number = higher accuracy.

Protection PT

Used for relays:

  • Class 3P
  • Class 6P

Protection PT focuses primarily on voltage fidelity during faults not billing accuracy.

Voltage Factor (Overvoltage Capability)

PT must withstand temporary overvoltages during:

  • Earth faults
  • Switching
  • Ferroresonance

System Earthing. Voltage Factor

Solidly earthed. 1.2 continuous

Isolated / unearthed. 1.9 for 8 hours

Always check utility / grid code requirement.

Insulation Level

PT insulation must match system BIL.

Example for 11 kV PT:

Rated insulation: 12/28/75 kV

  • 12 kV → highest system voltage
  • 28 kV → power frequency withstand
  • 75 kV → lightning impulse

PT Connection Types

Star–Star → Metering + protection

Open Delta (V-V) → Residual voltage (earth fault detection)

Broken Delta → Zero-sequence voltage (3V₀)

Typical PT Sizing

Example

System: 11 kV, solidly earthed

Secondary: 110 V

Total burden: 20 VA

Margin: 25%

Calculation:

20 x 1.25 = 25 VA

Final Selection:

  • PT Ratio: 11 kV / 110 V
  • VA Rating: 50 VA
  • Accuracy: 0.5 (metering) + 3P (protection)
  • Voltage Factor: 1.2 continuous.

You can also follow us on [color=#ff7700]AutomationForum.co[/color], [url= https://www.facebook.com/instrumentation.control][color=#1E00A3]Facebook[/color][/url] and [url= https://www.linkedin.com/showcase/81532759/feed/posts/][color=#1E00A3]Linkedin[/color][/url] to receive daily Instrumentation updates.