How to select the correct Potential Transformer rating for Protection and Metering?

A Potential Transformer (PT) steps down high system voltage to a safe, standardized low voltage for:

1). Metering (energy, voltage, power)

2). Protection relays

3). Control and indication circuits

It must:

• Maintain voltage accuracy

• Withstand system overvoltages

• Supply required VA burden without excessive error

PT Primary Voltage Selection

a) Based on System Voltage

Potential Transformer (PT) primary rating must match system phase voltage.

Voltage. PT Primary (Star)

11 KV 11 / √3 = 6.35kV

33 KV 33 / √3 = 19.05kV

66 kV 66 / √3 = 38.1kV

132 kV 132 / √3 = 76.2kV

Star-connected PTs are most common in most of substations.

PT Secondary Voltage Selection

Standard secondary voltages:

1). 110 V (most common)

2). 110 / √3 = 63.5 V (phase voltage)

3). 100 V (some standards)

Modern relays are designed for 110 V seconds.

PT Burden Calculation (IMP)

Burden is the total VA load connected to the Potential Transformer (PT) secondary.

It includes:

1). Protection relays

2). Metering devices

3). Indicating instruments

4). Cable losses

Device: Burden (VA)

Numerical protection relay: 10VA

Energy meter: 5 VA

Voltmeter: 2 VA

Selector switch + wiring: 3 VA

Total Actual Burden = 10 + 5 + 2 + 3 = 20 VA

Apply Engineering Margin

PT should never be operated at full rated burden.

Recommended margin:

20–30%

Required VA = 20 x 1.25 = 25VA

Selection of PT VA Rating

PTs are manufactured in standard VA ratings:

25 VA

50 VA

100 VA

200 VA

Always select the next higher standard rating.

Selected PT Rating = 50 VA

Accuracy Class Selection

Accuracy class defines maximum permissible voltage error.

Metering PT

Used for billing & measurement:

  • Class 0.2
  • Class 0.5

Lower number = higher accuracy.

Protection PT

Used for relays:

  • Class 3P
  • Class 6P

Protection PT focuses primarily on voltage fidelity during faults not billing accuracy.

Voltage Factor (Overvoltage Capability)

PT must withstand temporary overvoltages during:

  • Earth faults
  • Switching
  • Ferroresonance

System Earthing. Voltage Factor

Solidly earthed. 1.2 continuous

Isolated / unearthed. 1.9 for 8 hours

Always check utility / grid code requirement.

Insulation Level

PT insulation must match system BIL.

Example for 11 kV PT:

Rated insulation: 12/28/75 kV

  • 12 kV → highest system voltage
  • 28 kV → power frequency withstand
  • 75 kV → lightning impulse

PT Connection Types

Star–Star → Metering + protection

Open Delta (V-V) → Residual voltage (earth fault detection)

Broken Delta → Zero-sequence voltage (3V₀)

Typical PT Sizing

Example

System: 11 kV, solidly earthed

Secondary: 110 V

Total burden: 20 VA

Margin: 25%

Calculation:

20 x 1.25 = 25 VA

Final Selection:

  • PT Ratio: 11 kV / 110 V
  • VA Rating: 50 VA
  • Accuracy: 0.5 (metering) + 3P (protection)
  • Voltage Factor: 1.2 continuous.