A [url= Potential Transformer (PT) Testing Procedure][color=#1E00A3] Potential Transformer (PT) [/color][/url] steps down high system voltage to a safe, standardized low voltage for:
1). Metering (energy, voltage, power)
2). Protection relays
3). Control and indication circuits
It must:
• Maintain voltage accuracy
• Withstand system overvoltages
• Supply required VA burden without excessive error
PT Primary Voltage Selection
a) Based on System Voltage
Potential Transformer (PT) primary rating must match system [url= Line To Phase Voltage Calculator][color=#1E00A3] phase voltage. [/color][/url]
Voltage. PT Primary (Star)
11 KV 11 / √3 = 6.35kV
33 KV 33 / √3 = 19.05kV
66 kV 66 / √3 = 38.1kV
132 kV 132 / √3 = 76.2kV
Star-connected PTs are most common in most of substations.
PT Secondary Voltage Selection
Standard secondary voltages:
1). 110 V (most common)
2). 110 / √3 = 63.5 V (phase voltage)
3). 100 V (some standards)
Modern relays are designed for 110 V seconds.
PT Burden Calculation (IMP)
Burden is the total VA load connected to the Potential Transformer (PT) secondary.
It includes:
1). Protection relays
2). Metering devices
3). Indicating instruments
4). Cable losses
Device: Burden (VA)
Numerical protection [url= Phase Failure Relay (Voltage Monitoring Relay): Complete Guide for Three-Phase Motor Protection][color=#1E00A3] relay: [/color][/url] 10VA
Energy meter: 5 VA
Voltmeter: 2 VA
Selector switch + wiring: 3 VA
Total Actual Burden = 10 + 5 + 2 + 3 = 20 VA
Apply Engineering Margin
PT should never be operated at full rated burden.
Recommended margin:
20–30%
Required VA = 20 x 1.25 = 25VA
Selection of PT VA Rating
PTs are manufactured in standard VA ratings:
25 VA
50 VA
100 VA
200 VA
Always select the next higher standard rating.
Selected PT Rating = 50 VA
Accuracy Class Selection
Accuracy class defines maximum permissible voltage error.
Metering PT
Used for billing & measurement:
- Class 0.2
- Class 0.5
Lower number = higher accuracy.
Protection PT
Used for relays:
- Class 3P
- Class 6P
Protection PT focuses primarily on voltage fidelity during faults not billing accuracy.
Voltage Factor (Overvoltage Capability)
PT must withstand temporary overvoltages during:
- Earth faults
- Switching
- Ferroresonance
System Earthing. Voltage Factor
Solidly earthed. 1.2 continuous
Isolated / unearthed. 1.9 for 8 hours
Always check utility / grid code requirement.
Insulation Level
PT insulation must match system BIL.
Example for 11 kV PT:
Rated insulation: 12/28/75 kV
- 12 kV → highest system voltage
- 28 kV → power frequency withstand
- 75 kV → lightning impulse
PT Connection Types
Star–Star → Metering + protection
Open Delta (V-V) → Residual voltage (earth fault detection)
Broken Delta → Zero-sequence voltage (3V₀)
Typical PT Sizing
Example
System: 11 kV, solidly earthed
Secondary: 110 V
Total burden: 20 VA
Margin: 25%
Calculation:
20 x 1.25 = 25 VA
Final Selection:
- PT Ratio: 11 kV / 110 V
- VA Rating: 50 VA
- Accuracy: 0.5 (metering) + 3P (protection)
- Voltage Factor: 1.2 continuous.
You can also follow us on [color=#ff7700]AutomationForum.co[/color], [url= https://www.facebook.com/instrumentation.control][color=#1E00A3]Facebook[/color][/url] and [url= https://www.linkedin.com/showcase/81532759/feed/posts/][color=#1E00A3]Linkedin[/color][/url] to receive daily Instrumentation updates.