How to do the configuration of DP type flow meter in FF

Explain how to configure the DP flow meter in FF

check the transmitter range and DCS range, square root, first you see calibration datasheet, square & Linear type, then you set up and connect Hart and check the tag number, range input-output, after apply value transmitter range showing transmitter display and DCS output range square root, apply 25%, output showing 50.5%, you give 50% and DCS could show 70.7%, you give 75%, display and DCS could show 86.6%, you give 100%, display and DCS could show 100%.

For Foundation Fieldbus (FF), the Analog input block in the transducer group has the settings for pressure and flow.

L_Type is set to “Indirect” if the transmitter implements the square root function; Direct if the output is pressure, not flow.

XD_SCALE is the pressure range corresponding to 0-100% flow rate, according to the primary flow element sizing sheet. XD_SCALE is in units of percent.

OUT_SCALE is flow rate units and scaling LOW_CUT is low flow cut-off

OUT is the scaled flow output.