Equipment required:
Datasheet,
Pressure calibrator,
Multimeter,
Hart communicator
Procedure of DP Level Transmitter Calibration at field:
Man placed the computer in the control circuit manual mode and placed it on the ESD circuit MOS.
Refer to the datasheet to hook up HART Communicator and check some parameters. Typical parameters are PV, LRV and URV tag amount.
Isolate from the method of the tool.
Release both pressure and drain low and high side liquid throughout the manifold drain.
Open both plugs at seal pot.
Top up seal liquid for the low side until half of the seal pot.
Remove tubing at the high side of the manifold.
Hook up the calibrator on the at high side and isolate the vent valve
To evaluate the present signal, hook up a multimeter in sequence with the signal to the DCS.
If the amount equal to zero is applied as per calculation, the multimeter should display 4mA.
If not, use HART Communicator to adjust zero at the transmitter
Apply pressure according to the calculation if the amount is equal to 100%, the multimeter should show 20mA.
If not, use HART Communicator to adjust the receiver
After finishing the task, request the board driver to return loops to normal mode or to normalize the MOS.
Fill out and submit the calibration form for future reference.