Equipment required:
-
Datasheet,
-
Pressure calibrator,
-
Multimeter,
-
Hart communicator
Procedure of DP Level Transmitter Calibration at field:
-
Man placed the computer in the control circuit manual mode and placed it on the ESD circuit MOS.
-
Refer to the datasheet to hook up HART Communicator and check some parameters. Typical parameters are PV, LRV and URV tag amount.
-
Isolate from the method of the tool.
-
Release both pressure and drain low and high side liquid throughout the manifold drain.
-
Open both plugs at seal pot.
-
Top up seal liquid for the low side until half of the seal pot.
-
Remove tubing at the high side of the manifold.
-
Hook up the calibrator on the at high side and isolate the vent valve
-
To evaluate the present signal, hook up a multimeter in sequence with the signal to the DCS.
-
If the amount equal to zero is applied as per calculation, the multimeter should display 4mA.
-
If not, use HART Communicator to adjust zero at the transmitter
-
Apply pressure according to the calculation if the amount is equal to 100%, the multimeter should show 20mA.
-
If not, use HART Communicator to adjust the receiver
-
After finishing the task, request the board driver to return loops to normal mode or to normalize the MOS.
-
Fill out and submit the calibration form for future reference.