How to calculate kVAR from kW? Step-by-Step Calculation with Formula

Reactive power (kVAR) can be calculated from active power (kW) using the power factor of the electrical system. This calculation is essential for capacitor bank sizing, power factor correction, and electrical system design.

Formula to Calculate kVAR

kVAR = kW x tan(cos−1(Power Factor))​

Where:

  • kW = Active Power
  • Power Factor (PF) = Decimal value (e.g., 0.8, 0.9, 0.95)
  • kVAR = Reactive Power

Step-by-Step Calculation

Given:

  • Active Power = 100 kW
  • Power Factor = 0.80

Step 1: Find the phase angle

Θ = cos−1(0.80) = 36.87∘

Step 2: Calculate tan θ

tan(36.87∘) = 0.75

Step 3: Calculate reactive power

kVAR = 100 x 0.75 = 75 kVAR

Answer: Reactive Power = 75 kVAR

Why Calculate kVAR?

  • Size capacitor banks correctly
  • Improve power factor
  • Reduce reactive power penalties
  • Improve system efficiency
  • Optimize transformer and generator loading
  • Minimize power losses in electrical networks