How do you verify CT circuits?

How do you verify CT circuits?

Verifying current transformer (CT) circuits is essential for ensuring appropriate function & accuracy in electrical protection & metering systems. The CTs are tested for proper wiring, polarity, insulation, load, and operation.

Here is how to verify CT circuits:

1). Visual inspection

2). Polarity Test

3).Continuity Test

4). Insulation Resistance Test (IR Test)

5). Burden Test

6). Ratio Test

7). Secondary Injection Test

8). Loop Resistance Test

9). Excitation or Magnetization Curve Test

10). CT Circuit Load Check

11). Grounding Verification

12). Functional Test (Relay/Meter Response)

1). Visual inspection

Check for wire connections. Inspect the CT wiring & terminal connections for correct termination. Check for loose connections, corrosion, (or) damage.

Polarity check: Ensure that the right polarity is maintained, as this is essential for accurate measurement & protection. CT terminals are commonly labeled (P1, P2 for primary and S1, S2 for secondary).

2). Polarity Test

Check the polarity of the CTs using a polarity tester (or) a basic DC battery test.

Connect a battery to the primary terminals (P1, P2) and measure the output voltage across the secondary (S1, S2). The needle on the voltmeter will deflect in a specified direction to indicate polarity. Make sure it fits the CT polarity markings.

3).Continuity Test

Check for continuity in CT secondary circuits to ensure no open circuits (or) disconnections.

Use a multimeter to check the continuity of the S1 and S2 connections.

4). Insulation Resistance Test (IR Test)

Conduct an insulation resistance test utilizing a megger to check the CT winding insulation is intact. This test is conducted between the secondary winding & the soil.

Ensure that the insulating resistance is appropriate (usually in the megohms).

5). Burden Test

Ensure the load connected to the secondary winding is within the CT’s rated capacity.

Use a burden test set to determine the overall load on the secondary side, which includes the cables, meters, and relays. Ensure it does not exceed the CT’s assessed burden.

6). Ratio Test

Conduct a ratio test to confirm the CT steps down the current according to its rating. You can inject a known current into the primary winding & measure the resulting secondary current.

Utilize a primary injection test set for this. The primary-to-secondary current ratio must correspond to the CT’s set ratio (for example, 1000:1, 500:5).

7). Secondary Injection Test

If primary injection is not possible, inject a known current into the secondary circuit to evaluate the reaction of linked relays or meters.

8). Loop Resistance Test

Use a micro-ohmmeter to confirm the CT secondary loop’s resistance is within acceptable limits. Excessive loop resistance may indicate improper wiring or connections.

9). Excitation or Magnetization Curve Test

Conduct an excitation (or) magnetization curve test to establish the knee point voltage and confirm proper CT performance during fault conditions.

This test helps to ensure that the CT can enter saturation properly and is suitable for protective class CTs.

10). CT Circuit Load Check

Ensure the secondary circuit load does not exceed the CT’s rated load. The burden includes the impedance of the associated devices (meters, relays, etc.).

11). Grounding Verification

Ground the CT secondary winding at a single place (typically the relay or meter) to prevent circulating current.

12). Functional Test (Relay/Meter Response)

Ensure linked protective relays or meters are working properly by simulating fault (or) load conditions & evaluating their response.

Following these steps ensures that the CT circuit is accurate and reliable for both protection & metering.