Difference Between Selectivity and Cascading in Electrical Design

Difference Between Selectivity and Cascading in Electrical Design

Selectivity

Selectivity is defined as the ability of a protective system to isolate only the problematic portion of the network while keeping the remainder of the system operational. It minimize the impact of a fault by tripping only the nearest breaker or fuse.

Ex: If there is a short circuit in a motor feeder, just the feeder breaker must trip, not the main breaker.

Outcome: Increased supply dependability and continuity.

Types of Selectivity:

  1. Current selectivity

  2. Time selectivity

  3. Energy selectivity (fuses)

  4. Zone selectivity (for relays and breakers)

Cascading (Backup Protection and Series Rating)

Cascading is the coordination of two protective devices (usually upstream & downstream circuit breakers or fuses), with the upstream device supporting the downstream device’s breaking capacity.

The purpose is to allow the utilization of downstream devices with the lower short-circuit ratings while depending on the upstream device to clear high fault currents.

Ex: A small breaker with a 10 kA rating can be utilized downstream of a 50 kA main breaker, as the main breaker will limit fault current when severe short circuits occurs.

As a result, costs are reduced (smaller devices can be utilized), but the manufacturer must test and approve the pair as one.

Difference Between Selectivity and Cascading

Selectivity vs Cascading

Aspect Selectivity (Discrimination) Cascading (Back-up Protection / Series Rating)
Definition Ensures only the faulty circuit breaker/fuse trips, keeping the rest of the system running. Coordination where the upstream breaker supports the breaking capacity of the downstream breaker.
Objective Improve reliability and continuity of supply by isolating only the fault. Allow use of downstream devices with lower short-circuit rating, reducing cost.
Focus Who trips during a fault. Who protects whom during a fault.
Fault Handling The nearest protection device to the fault operates. Upstream breaker helps interrupt high fault current that downstream breaker cannot handle alone.
Types Current, Time, Energy, and Zone Selectivity. Series-rated / Back-up protection tested by manufacturers.
Application Critical in industrial plants, hospitals, data centers (where continuity is vital). Useful in commercial/industrial boards where cost optimization is needed.
Result Selective tripping → continuity of supply. Cost saving → smaller devices can be used safely.
Example A motor feeder trips without affecting the main breaker. A 10 kA downstream breaker works safely with a 50 kA upstream breaker.