CT Nameplate Parameters

CT NAMEPLATE PARAMETERS

1). Rated Primary Current (Ip)

Example:

• 400 A

• 800/400/200 A (multi-ratio)

2). Rated Secondary Current (Is)

• 5A (most common for LV/MV panels)

• 1A (long cable runs, reduces burden losses)

3). CT Ratio

Example:

• 400/5

• 800/1

If multi-ratio:

• 800-400-200/1

4). Burden (VA)

Example:

• 5 VA

• 10 VA

• 15 VA

• 30 VA

This means the CT can supply that many volt-amperes without exceeding accuracy limits.

5). Accuracy Class

Examples:

• Metering: 0.2, 0.5, 1.0

• Protection: 5P10, 5P20, 10P10

• Special: PX, PR

6). Frequency

• 50 Hz (India)

• 60 Hz (US)

7). Insulation Level

Example for 11 kV CT:

• 12/28/75 kV

Meaning

• 12 kV → rms working

• 28 kV → 1-min power-frequency withstand

• 75 kV → lightning impulse withstand

8). Thermal Short-Time Current (Ith)

CT must survive short-circuit for 1 second.

Example:

• 25 kA, 1 sec

• 31.5 kA, 1 sec

9). Dynamic Current (Idyn)

Withstand peak current (electrodynamic forces).

Typically:

I_dyn = 2.5 x I_th

Example:

If Ith = 25 kA → Idyn ≈ 62.5 kA

10). Knee Point Voltage (Vk) (ONLY for PX class)

Example:

• Vk ≥ 120 V

• Vk ≥ 150 V

Important for differential relay operation.

11). Magnetizing Current (Im)

Typical:

• ≤ 30 mA at Vk/2

12). Secondary Winding Resistance (Rct)

Given in ohms.

Used for checking:

• Volt-drop

• CT saturation

• Relay burden calculation

13). Polarity Marking (P1, P2, S1, S2)

Important for CT orientation.

• P1 → Towards the source

• P2 → Towards the load

• S1 → Relay/meter positive

• S2 → Common/neutral

14). CT Type

• Wound type

• Bar type

• Ring type (core type)

15). Thermal Rating Factor (TRF)

Example:

• 1.2 times continuous current

Means CT can carry 20% overload continuously.

16). Standards (IS/IEC)

• IEC 61869-2

• IS 16227-2 1. Rated Primary Current (Ip)