Calculate the output in mA of Electronics D.P Tx. When applied a D.P of 125 inches of water gauge, knowing that the range is 0 to 300 inches of WG?
To calculate the output current in mA for an electronic differential pressure transmitter (D.P Tx) with a range of 0 to 300 inches of water gauge (WG), you can use the following formula:
Where:
- ( DP ) is the differential pressure applied.
- ( LRV ) is the lower range value, which is 0 inches of WG in this case.
- ( URV ) is the upper range value, which is 300 inches of WG.
- ( Span ) is the difference between the maximum and minimum output current, which is typically 16 mA (20 mA - 4 mA for a 4-20 mA transmitter).
Given that the applied ( DP ) is 125 inches of WG, the calculation would be:
So, the output current would be 10.667 mA when a differential pressure of 125 inches of WG is applied to the transmitter.