Cable Megger Testing

Cable Megger Testing

Cable Megger Testing, which is also referred as insulation resistance (IR) testing, is a key method used on electrical cables to assess the quality and dependability of its insulation. It assists in the detection of

  • Insulation deterioration,
  • Moisture infiltration,
  • Contamination, and
  • Other internal problems

that may result in breakdowns or electrical issues.

This test is performed using a specialized device known as a Megger (Insulation Resistance Tester).

Objective of Cable Megger Testing

The fundamental objective of Megger testing is to confirm that the cable insulation is in good condition and can sustain the applied operational voltage. It protects against hazards such as

  • Short circuits,
  • Leakage currents,
  • Electric shocks and
  • Equipment failure.

The electrical system’s safety is ensured by determining the insulation resistance across conductors as well as conductor-to-earth.

Safety Precautions

Before testing, always confirm that the cable has been deenergized.

After testing, discharge the cable as it may still contain a significant DC voltage.

To avoid electric shock threats, use suitable PPE.

Ensure that the test environment is dry & safe.Working Principle of Megger Testing

The Megger operates by putting a high DC voltage (often 250V to 5kV, depending on the system rating) between the insulation & measuring the resistance provided.

A good insulation will have a very high resistance (in megaohms), whereas a poor insulation will have a low resistance signaling possible problems.

Test Procedure

Step-1: Disconnect the cable from the power supply & make sure it is de-energized.

Step-2: Connect one lead of Megger to conductor & the other to earth.

Step-3: Choose the correct test voltage (typically 500V for low-voltage cables and 1kV or higher for medium/high voltage cables).

Step-4: Record the insulating resistance reading that appears on the Megger.

Step-5: Repeat the test for all conductors with regard to each other and ground.

Acceptance Conditions

Insulation resistance for low-voltage (LV) systems (up to 1 kV) typically exceeds 1 MΩ.

Resistance ratings for medium & high-voltage cables are predicted to be in the hundreds of megaohms range.

Readings that are much lower than the usual value suggest moisture, insulation degradation, or contamination.

You can also follow us on AutomationForum.co, Facebook and Linkedin to receive daily Instrumentation updates.