> # Why is the X/ R ratio taken as 14? (In short Circuit Analysis)

There is no standard for X/R ratio.

 ![image](https://cdn.forumautomation.com/original/2X/b/bdc1e45ffffd9f0d592296d7b2a869e6d0c37546.jpeg)

But time constant t = L/R

In power system we have taken t = (X/R) /(2πf)

As per **[IEC 62271](https://webstore.iec.ch/en/publication/6740)**; time constant value is 45 ms.

t = 45 ms.

t = (X/R) /(2πf)

0.045 = (X/R)/ (2 x 3.142 x 50)

X/R = 0.045 \* (2 x 3.142 x 50)

X/R = 14.137 (approximately equal to 14)

- **X/R = 14 for 50 Hz system**
- **X/R = 17 for 60 Hz system.**