# Why the phase to phase is 415V and phase to neutral is 190V?

**URL:** <https://forumautomation.com/t/why-the-phase-to-phase-is-415v-and-phase-to-neutral-is-190v/9818>\
**Category:** Electrical\
**Tags:** electrical\
**Created:** [September 4, 2021, 10:33am UTC](https://forumautomation.com/t/why-the-phase-to-phase-is-415v-and-phase-to-neutral-is-190v/9818 "2021-09-04T10:33:46Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [September 4, 2021, 10:33am UTC](https://forumautomation.com/t/why-the-phase-to-phase-is-415v-and-phase-to-neutral-is-190v/9818/1 "2021-09-04T10:33:46Z")

</div>

Explain why the phase to phase is 415V and the phase to neutral is 190V?

 ![1](https://cdn.forumautomation.com/original/2X/5/5556c8992c2a9523516170afab6fe4a8ad59d509.jpeg)

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [September 4, 2021, 10:40am UTC](https://forumautomation.com/t/why-the-phase-to-phase-is-415v-and-phase-to-neutral-is-190v/9818/2 "2021-09-04T10:40:15Z")

</div>

1. 415/√3=240V approximately.

Your line to neutral should be 240 V. In phase to neutral the voltage measurement is done with respect to neutral and that’s why **[phase to phase](https://forumelectrical.com/220v-three-phase-electrical-wiring-purpose-features-and-practical-uses/)** and phase to neutral have different voltage measurement.

Check there must be a leakage in your circuits. Test N to E, the difference will be found there. To check N to E you have to ensure that Transformer Neutral is connected with Earth.

1. If you are using a small cross-sectional area cable for a long-distance load, it’s possible because of voltage drop. In that case, you need to determine the drop based on your cable size and select a bigger cable with minimal voltage drop.