# Why O:2/0 is used at the bottom of start in a ladder diagram

**URL:** <https://forumautomation.com/t/why-o-2-0-is-used-at-the-bottom-of-start-in-a-ladder-diagram/9336>\
**Category:** PLC (Programmable Logic Controllers)\
**Created:** [April 19, 2021, 2:15am UTC](https://forumautomation.com/t/why-o-2-0-is-used-at-the-bottom-of-start-in-a-ladder-diagram/9336 "2021-04-19T02:15:27Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [April 19, 2021, 2:15am UTC](https://forumautomation.com/t/why-o-2-0-is-used-at-the-bottom-of-start-in-a-ladder-diagram/9336/1 "2021-04-19T02:15:28Z")

</div>

What is the need for using O:2/0 at the bottom of start

 ![image](https://cdn.forumautomation.com/original/2X/1/197d1050788e337162e3a4b51ca3df387a201094.jpeg)

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [April 19, 2021, 2:19am UTC](https://forumautomation.com/t/why-o-2-0-is-used-at-the-bottom-of-start-in-a-ladder-diagram/9336/2 "2021-04-19T02:19:34Z")

</div>

It’s a latch used to hold the output on once the momentary start button is pushed.

It is used for holding the logic ON state.

When you press START I:1/0 the Output O:2/0 gets ON. But when you release the I:1/0 the Output 0:2/0 will also get OFF.

When you put holding condition(O:2/0) parallel to I:1/0 even if it turns OFF the output will remain ON state. Till you Turn ON STOP I:1/2 input