# Why is the o/p range for the majority of analog devices 4 to 20 mA rather than 0 to 20 mA?

**URL:** <https://forumautomation.com/t/why-is-the-o-p-range-for-the-majority-of-analog-devices-4-to-20-ma-rather-than-0-to-20-ma/12304>\
**Category:** Field Instrumentation\
**Tags:** interviewquestions\
**Created:** [July 21, 2024, 8:35am UTC](https://forumautomation.com/t/why-is-the-o-p-range-for-the-majority-of-analog-devices-4-to-20-ma-rather-than-0-to-20-ma/12304 "2024-07-21T08:35:09Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![Instrument\_Engineer](https://forumautomation.com/user_avatar/forumautomation.com/instrument_engineer/32/6734_2.png) [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Post date:** [July 21, 2024, 8:35am UTC](https://forumautomation.com/t/why-is-the-o-p-range-for-the-majority-of-analog-devices-4-to-20-ma-rather-than-0-to-20-ma/12304/1 "2024-07-21T08:35:09Z")

</div>

Why most of analog o/p devices having o/p range 4 to 20 mA and not 0 to 20 mA?

 ![image](https://cdn.forumautomation.com/original/2X/5/58ffbd918c4762041ca707861c7fab27014b748f.jpeg)

---

<div class="post-metadata">

**Author:** ![automation\_engineer6](https://forumautomation.com/user_avatar/forumautomation.com/automation_engineer6/32/7656_2.png) [@automation\_engineer6](https://forumautomation.com/u/automation_engineer6)\
**Post date:** [July 23, 2024, 4:30pm UTC](https://forumautomation.com/t/why-is-the-o-p-range-for-the-majority-of-analog-devices-4-to-20-ma-rather-than-0-to-20-ma/12304/2 "2024-07-23T16:30:16Z")

</div>

The 4-20 mA range is preferred over 0-20 mA for most analog devices in industrial settings for several practical reasons:

1. Fault detection: A 0 mA reading clearly indicates a problem like a broken wire or power loss.
2. Powering transmitters: The 4 mA minimum provides power for two-wire transmitters, even at minimum readings.
3. Noise resistance: Starting at 4 mA gives better protection against electrical interference, especially over long distances.
4. Easier calibration: The 4 mA “live zero” makes it simpler to adjust the zero point without confusing it with a fault.
5. Better accuracy: Using 4-20 mA increases measurement resolution since the same 16 mA span represents the full range.
6. Wide compatibility: The 4-20 mA standard is widely used, making it easier to integrate devices from different manufacturers.

These advantages make 4-20 mA loops more reliable and practical for industrial applications, which is why they’re generally chosen over 0-20 mA systems. Refer the below link for the detailed explanation

> **[Why not use 0-20mA & 0-15psi instead of 4-20mA & 3-15psi?](https://automationforum.co/why-not-use-0-20ma-0-15psi-instead-of-4-20ma-3-15psi/)**
>
> The 4-20 mA and 3-15 psi standards offer advantages like fault detection, cost efficiency, and easier pressure regulation in industrial instrumentation