# What is the typical setting range of an overvoltage relay in power systems?

**URL:** <https://forumautomation.com/t/what-is-the-typical-setting-range-of-an-overvoltage-relay-in-power-systems/13829>\
**Category:** Electrical\
**Created:** [January 16, 2026, 1:42pm UTC](https://forumautomation.com/t/what-is-the-typical-setting-range-of-an-overvoltage-relay-in-power-systems/13829 "2026-01-16T13:42:18Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Rabert](https://forumautomation.com/user_avatar/forumautomation.com/rabert/32/6784_2.png) [@Rabert](https://forumautomation.com/u/Rabert)\
**Post date:** [January 16, 2026, 1:42pm UTC](https://forumautomation.com/t/what-is-the-typical-setting-range-of-an-overvoltage-relay-in-power-systems/13829/1 "2026-01-16T13:42:18Z")

</div>

The typical setting range of an overvoltage relay (**[ANSI 59](https://forumelectrical.com/ansi-standards/)**) in power systems depends on the application level and the system voltage but standard practice follows the well accepted protection guidelines.

## Typical Overvoltage Relay Settings

| **Application Area** | **Pickup Setting (per unit)** | **Time Delay** |
| --- | --- | --- |
| Generator terminals | **1.05 - 1.10 pu** | 1 - 10 s |
| Transmission lines | **1.10 - 1.20 pu** | 0.2 - 2 s |
| Distribution feeders | **1.10 - 1.25 pu** | 0.1 - 1 s |
| Motors | **1.05 - 1.15 pu** | 1 - 5 s |
| Capacitor banks | **1.10 - 1.30 pu** | 0 - 0.5 s (fast) |

**[Per unit (pu)](https://forumautomation.com/t/what-is-pu-in-electrical-engineering/10906)** is based on rated system voltage (1.0 pu = 100% rated voltage).

 ![image](https://cdn.forumautomation.com/original/2X/6/637e98baedc71b07515e4afef06964bb2a7f2e5a.jpeg)

## Practical Example

For an 11 kV system:

1.10 pu = 12.1 kV

1.20 pu = 13.2 kV

So the overvoltage relay may be set to trip between 12.1 kV and 13.2 kV depending on the protection methods.

## Why not set too low?

To avoid nuisance tripping due to the normal voltage fluctuations.

To allow AVR tap changes and system transients.

## Why not set too high?

Used to prevent insulation stress.

To protect equipment (transformers, motors, surge arresters).

> ### You can also follow us on [[color=#ff7700] **AutomationForum.co** [/color]](https://automationforum.co/), [url= [https://www.facebook.com/instrumentation.control](https://www.facebook.com/instrumentation.control)][color=#1E00A3] **Facebook** [/color][/url] and [url= [https://www.linkedin.com/showcase/81532759/feed/posts/](https://www.linkedin.com/showcase/81532759/feed/posts/)][color=#1E00A3] **Linkedin** [/color][/url] to receive daily Instrumentation updates.

> ### You can also follow us on [[color=#ff7700] **ForumElectrical.com** [/color]](https://forumelectrical.com/), [[color=#1E00A3] **Facebook** [/color]](https://www.facebook.com/profile.php?id=100091841583670) and [[color=#1E00A3] **Linkedin** [/color]](https://www.linkedin.com/showcase/91130242/feed/posts/) to receive daily Electrical updates.