# What is the purpose of wet leg in DP type level transmitter

**URL:** <https://forumautomation.com/t/what-is-the-purpose-of-wet-leg-in-dp-type-level-transmitter/9539>\
**Category:** Field Instrumentation\
**Created:** [June 25, 2021, 10:17am UTC](https://forumautomation.com/t/what-is-the-purpose-of-wet-leg-in-dp-type-level-transmitter/9539 "2021-06-25T10:17:38Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [June 25, 2021, 10:17am UTC](https://forumautomation.com/t/what-is-the-purpose-of-wet-leg-in-dp-type-level-transmitter/9539/1 "2021-06-25T10:17:38Z")

</div>

Explain the need for wet-leg in DP type level transmitter

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [June 25, 2021, 10:20am UTC](https://forumautomation.com/t/what-is-the-purpose-of-wet-leg-in-dp-type-level-transmitter/9539/2 "2021-06-25T10:20:38Z")

</div>

- It would prevent the process from directly acting on the transmitter diaphragm
- if process condition change due to ambient temperature then use wet leg
- Prevent the transmitter diaphragm from chemical or stem process
- If the wet leg is elevated then no matter density the measured valve will be accurate

---

<div class="post-metadata">

**Author:** ![carl\_e](https://forumautomation.com/letter_avatar_proxy/v4/letter/c/94ad74/32.png) [@carl\_e](https://forumautomation.com/u/carl_e)\
**Post date:** [July 7, 2021, 10:15pm UTC](https://forumautomation.com/t/what-is-the-purpose-of-wet-leg-in-dp-type-level-transmitter/9539/3 "2021-07-07T22:15:12Z")

</div>

> [@ashlin](#):
>
> - If the wet leg is elevated then no matter density the measured valve will be accurate

I’m not exactly what the claim is. It sounds like a claim that a wet can compensate for process medium density in the vessel.

Elevation just adds or subtracts a fixed constant from wet leg pressure side.

A wet leg does offer a fixed reference level/pressure isolated from the process, as long as the process does not merge/mix with the fill fluid and and in so doing, change the wet leg fill density.

But even an unpolluted wet leg with a known density can not compensate for density changes in the vessel under measurement.