# What is the procedure for calibrating the flowserve logix500 si series ip positioner?

**URL:** <https://forumautomation.com/t/what-is-the-procedure-for-calibrating-the-flowserve-logix500-si-series-ip-positioner/12114>\
**Category:** Calibration\
**Tags:** interviewquestions\
**Created:** [May 30, 2024, 8:05pm UTC](https://forumautomation.com/t/what-is-the-procedure-for-calibrating-the-flowserve-logix500-si-series-ip-positioner/12114 "2024-05-30T20:05:06Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![Sundar\_Iyalunaidu](https://forumautomation.com/user_avatar/forumautomation.com/sundar_iyalunaidu/32/7404_2.png) [@Sundar\_Iyalunaidu](https://forumautomation.com/u/Sundar_Iyalunaidu)\
**Post date:** [May 30, 2024, 8:05pm UTC](https://forumautomation.com/t/what-is-the-procedure-for-calibrating-the-flowserve-logix500-si-series-ip-positioner/12114/1 "2024-05-30T20:05:06Z")

</div>

What is the procedure for calibrating the flowserve logix500 si series ip positioner?

 ![image](https://cdn.forumautomation.com/original/2X/d/d223e6383b340174f246e48f5c8d3ff81d57b6e0.jpeg)

---

<div class="post-metadata">

**Author:** ![Instrument\_Engineer](https://forumautomation.com/user_avatar/forumautomation.com/instrument_engineer/32/6734_2.png) [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Post date:** [June 7, 2024, 5:18am UTC](https://forumautomation.com/t/what-is-the-procedure-for-calibrating-the-flowserve-logix500-si-series-ip-positioner/12114/2 "2024-06-07T05:18:21Z")

</div>

![image](https://cdn.forumautomation.com/original/2X/2/2eb1d6cd2550cdbabcf310b9723a3813d882cd00.png)To calibrate the Flowserve Logix 500si series digital positioner:

1. **Press the QUICK-CAL button** to easily and quickly calibrate the positioner on all actuators without physical stroke stops.
2. **The calibration process will be completed** when the lights return to a sequence that starts with a green light.
3. **Commissioning is performed** by simply setting a few switches and pressing the QUICK-CAL button. The Direct User Interface provides local access to positioner control without requiring multi-level menus, a handheld communicator or laptop computer.
4. **Fast calibration and setup** can be made by simply pressing the Quick-Cal button. Interchangeable components (such as circuit board, piezo drivers, etc.) allow for easy maintenance.

---

<div class="post-metadata">

**Author:** ![Instrument\_Engineer](https://forumautomation.com/user_avatar/forumautomation.com/instrument_engineer/32/6734_2.png) [@Instrument\_Engineer](https://forumautomation.com/u/Instrument_Engineer)\
**Post date:** [June 7, 2024, 5:23am UTC](https://forumautomation.com/t/what-is-the-procedure-for-calibrating-the-flowserve-logix500-si-series-ip-positioner/12114/3 "2024-06-07T05:23:13Z")

</div>

The Flowserve Logix 500 SI Series I/P positioner requires multiple steps to calibrate. The following is a generic process outline to help you through it:

### Tools and Equipment Needed:

- Flowserve Logix 500 SI Series I/P positioner
- Handheld communicator or calibration device (such as HART communicator)
- Power supply (if necessary)
- Appropriate documentation (e.g., the user manual for the specific model)

### Calibration Procedure:

1. **Safety Precautions:**

- Ensure that the valve and actuator system is depressurized and de-energized before starting.
- Follow all relevant safety guidelines and lockout/tagout procedures.

1. **Setup:**

- Connect the handheld communicator to the positioner. If using a HART communicator, connect it to the current loop.
- Ensure that the positioner is properly installed on the actuator and that the air supply is connected and regulated to the correct pressure.

1. **Power On:**

- Power on the positioner and the handheld communicator. Wait for the devices to initialize.

1. **Enter Calibration Mode:**

- Use the communicator to navigate to the calibration mode on the positioner. This might involve accessing a specific menu or pressing a combination of buttons.

1. **Zero Calibration:**

- Set the input signal to 4 mA (or the lower range value, typically corresponding to 0% position).
- Ensure that the valve is in the fully closed position.
- Initiate the zero calibration process via the communicator. The positioner will adjust itself to recognize the fully closed position as 0%.

1. **Span Calibration:**

- Set the input signal to 20 mA (or the upper range value, typically corresponding to 100% position).
- Ensure that the valve is in the fully open position.
- Initiate the span calibration process via the communicator. The positioner will adjust itself to recognize the fully open position as 100%.

1. **Intermediate Points:**

- Some positioners may require calibration at intermediate points (e.g., 25%, 50%, 75%). Follow the prompts on the communicator to set these points if necessary.

1. **Verification:**

- After calibration, verify that the positioner correctly responds to the full range of input signals (e.g., 4 mA to 20 mA) and that the valve moves accurately to the corresponding positions.
- Look for any alarms or error messages on the positioner or communicator display. Keep and Leave:.

1. **Save and Exit:**

- Save the calibration settings if prompted by the communicator.
- Exit the calibration mode and return the positioner to normal operating mode.

1. **Documentation:**

- Record the calibration results and any observations for future reference.

### Troubleshooting:

- If the positioner does not respond correctly during calibration, check the air supply, wiring, and connections.
- Refer to the user manual for specific troubleshooting steps related to your model.

Always refer to the specific user manual for the Flowserve Logix 500 SI Series I/P positioner you are using, as there may be model-specific steps or variations in the procedure.