## What is the Normally Permitted Motor Ratings as per DEWA?

Motor ratings are regulated by the **Dubai Electricity and Water Authority (DEWA)** to minimize starting current, voltage drop and system disturbance. The typically permissible motor ratings (without special approval or additional starting procedures) are shown below:

 ![image](https://cdn.forumautomation.com/original/2X/7/752ebce0b6d6eebfbbef38bc61940d211e70bc07.jpeg)

Normally Permitted Motor Ratings (LV – 415 V, 3-Phase)

## 1). Direct-On-Line (DOL) Starter

| **Motor Rating** | **Permission Status** |
| --- | --- |
| **Up to 7.5 kW (10 HP)** | Normally permitted |
| **\> 7.5 kW** | Not permitted with DOL (approval required) |

**Note:** DOL starting draws 6-7 times the rated current resulting in voltage drops that are inappropriate for heavier motors.

## 2). Star–Delta Starter

| **Motor Rating** | **Permission Status** |
| --- | --- |
| **7.5 kW to 30 kW (10–40 HP)** | Normally permitted |
| **\> 30 kW** | Requires DEWA approval / justification |

## 3). Soft Starter

| **Motor Rating** | **Permission Status** |
| --- | --- |
| **Up to 75 kW** | Generally permitted |
| **\> 75 kW** | Subject to DEWA study & approval |

## 4). Variable Frequency Drive (VFD / VSD)

| **Motor Rating** | **Permission Status** |
| --- | --- |
| **Up to 150 kW** | Normally permitted |
| **\> 150 kW** | DEWA load study & approval required |

**Note:** **[VFDs](https://forumelectrical.com/vfd-control-circuit-testing-step-by-step-procedure-for-reliable-drive-operation/)** are popular because they require less starting current and provide regulated acceleration.

> ### You can also follow us on [[color=#ff7700] **AutomationForum.co** [/color]](https://automationforum.co/), [url= [https://www.facebook.com/instrumentation.control](https://www.facebook.com/instrumentation.control)][color=#1E00A3] **Facebook** [/color][/url] and [url= [https://www.linkedin.com/showcase/81532759/feed/posts/](https://www.linkedin.com/showcase/81532759/feed/posts/)][color=#1E00A3] **Linkedin** [/color][/url] to receive daily Instrumentation updates.

> ### You can also follow us on [[color=#ff7700] **ForumElectrical.com** [/color]](https://forumelectrical.com/), [[color=#1E00A3] **Facebook** [/color]](https://www.facebook.com/profile.php?id=100091841583670) and [[color=#1E00A3] **Linkedin** [/color]](https://www.linkedin.com/showcase/91130242/feed/posts/) to receive daily Electrical updates.