Explain how a lower trim is different from a zero trim

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [February 10, 2021, 10:01am UTC](https://forumautomation.com/t/what-is-the-difference-between-zero-trim-and-lower-trim/9154/2 "2021-02-10T10:01:28Z")

</div>

Zero trim use for pressure reset in open to atmosphere condition in the transmitter

Lower and upper trim is used in conditions where an error in reading in a calibration range is different from reading.

For example:

If the range of a pressure transmitter is 0 to 10 bar and -25mmH2O to +25mmH20.

While you calibrate the transmitter which is 0 to 10 bar, to carry out the zero calibration you need to zero trim in Hart communicator with zero pressure g to the transmitter (open to atmosphere)

For the range -25mmH2O to +25mmH2O you need to give negative pressure of -25mmH2o to the transmitter (HP side if it is DP transmitter) and do a lower-trim from Hart communicator for the zero calibration.

Hence the zero trim is required for the TX range starts from exactly zero ( 0-10bar) and lower trim is required for the TX range starts below or above zero eg. -25mmH2O to +25mmH2o or 25 mmH2O to125 mmH2O.