# What are the calibration tolerances for Pressure Switch /Temperature Switch /Level Switch?

**URL:** <https://forumautomation.com/t/what-are-the-calibration-tolerances-for-pressure-switch-temperature-switch-level-switch/979>\
**Category:** Field Instrumentation\
**Created:** [April 12, 2016, 12:56am UTC](https://forumautomation.com/t/what-are-the-calibration-tolerances-for-pressure-switch-temperature-switch-level-switch/979 "2016-04-12T00:56:03Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![denizen](https://forumautomation.com/letter_avatar_proxy/v4/letter/d/848f3c/32.png) [@denizen](https://forumautomation.com/u/denizen)\
**Post date:** [April 12, 2016, 12:56am UTC](https://forumautomation.com/t/what-are-the-calibration-tolerances-for-pressure-switch-temperature-switch-level-switch/979/1 "2016-04-12T00:56:03Z")

</div>

Calibration tolerances are based on process requirements and do not use manufacture accuracy specification.

Pressure Switch Calibration Tolerances -

-Generally +/- 1 psig for pressure switch with setpoint \< 100 psig -Wider tolerance ok depending on purpose -Tolerance N/A for reset point unless critical to process.

Temperature Switch

-Generally +/- 1 deg C is for RTD input. 2 deg C for thermocouple input.Wider for filled bulb and extreme temperatures if process requirement allows.

Level switch

- +/- 1 inch

Flow Switches

+/-5 %