# Understanding the IEC Standards for Earthing Systems

**URL:** <https://forumautomation.com/t/understanding-the-iec-standards-for-earthing-systems/12891>\
**Category:** Electrical\
**Tags:** standard\
**Created:** [December 10, 2024, 6:11am UTC](https://forumautomation.com/t/understanding-the-iec-standards-for-earthing-systems/12891 "2024-12-10T06:11:23Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Rabert](https://forumautomation.com/user_avatar/forumautomation.com/rabert/32/6784_2.png) [@Rabert](https://forumautomation.com/u/Rabert)\
**Post date:** [December 10, 2024, 6:11am UTC](https://forumautomation.com/t/understanding-the-iec-standards-for-earthing-systems/12891/1 "2024-12-10T06:11:23Z")

</div>

[**Earthing**](https://forumelectrical.com/what-is-earthing-explain-its-procedure-and-their-advantages/) is a safety precaution that involves connecting an electrical system to the surface of the ground. It allows electrical current to pass safely to ground in the event of a fault or overload, lowering the risk of electrocution, fire, & equipment damage.

 ![1](https://cdn.forumautomation.com/original/2X/0/05b3dbf0ec2c96e8811d62e7ee15337744d4452e.jpeg)

The International standard [**IEC 60364**](https://webstore.iec.ch/en/publication/1865) defines 3 types of earthing arrangements:

1). TN

2). TT

3). IT

- The first letter shows how the earthing is done on the source side (generator/transformer).
- The Second Letter specifies how the Earthing is done on the device side.
- ‘T’ indicates that direct connection of a point to the ground.
- ‘I’ indicates that either no point is linked to Earth (or) it is connected via a high impedance.
- ‘N’ indicates that there is a direct connection to neutral at source of installation, which is then connected to the ground.

> ## 1). TN Earthing System

- Three types of TN earthing systems exist, according on how the neutral & protective conductors are fed.
- The TN-S system makes use of a separate protecting conductor.
- TN-C-S system: The neutral & protective conductors are merged into a single conductor in a system component.
- TN-C system: The neutral & protecting conductors are integrated into a single conductor in the entire system.

> ## 2). TT Earthing System

- The neutral is directly earthed on the source side.
- The consumer is powered via a local earth electrode.

> ## 3). IT Earthing System

- The power supply is either not earthed (or) earthed with a high impedance.
- The exposed conductive portions of the system are connected to ground independently of the power source.