## Transformer Short-Circuit Current and Percentage Impedance Calculation

Transformer full-load current is determined by its rated kVA and operating voltage. The percentage impedance (%Z) is used to estimate the prospective **[short-circuit current](https://forumelectrical.com/transformer-short-circuit-current-calculation/)** at the transformer terminals.

 ![1](https://cdn.forumautomation.com/original/2X/a/ac249b15fb3efb0d91ce15e4fb094a8f87eabd02.jpeg)

## Calculation Formulas

**Three-Phase Full-Load Current:** I\_FL = (kVA × 1,000) / (√3 × V)

**Transformer-Terminal Short-Circuit Current:** I\_SC = I\_FL × (100 / %Z)