# The digital input signals connected to the digital input module have normally open contacts. Does this module detect Earth faults on these inputs signals

**URL:** <https://forumautomation.com/t/the-digital-input-signals-connected-to-the-digital-input-module-have-normally-open-contacts-does-this-module-detect-earth-faults-on-these-inputs-signals/185>\
**Category:** Honeywell\
**Created:** [December 6, 2014, 5:11pm UTC](https://forumautomation.com/t/the-digital-input-signals-connected-to-the-digital-input-module-have-normally-open-contacts-does-this-module-detect-earth-faults-on-these-inputs-signals/185 "2014-12-06T17:11:46Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![omega](https://forumautomation.com/letter_avatar_proxy/v4/letter/o/a6a055/32.png) [@omega](https://forumautomation.com/u/omega)\
**Post date:** [December 6, 2014, 5:11pm UTC](https://forumautomation.com/t/the-digital-input-signals-connected-to-the-digital-input-module-have-normally-open-contacts-does-this-module-detect-earth-faults-on-these-inputs-signals/185/1 "2014-12-06T17:11:47Z")

</div>

The Safety system has a Earth Leakage Detector module (10310/./1) installed. The digital input signals connected to the digital input module have normally open contacts. Does this module detect Earth faults on these inputs signals.

---

<div class="post-metadata">

**Author:** ![instrumen](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/65b543/32.png) [@instrumen](https://forumautomation.com/u/instrumen)\
**Post date:** [December 6, 2014, 5:16pm UTC](https://forumautomation.com/t/the-digital-input-signals-connected-to-the-digital-input-module-have-normally-open-contacts-does-this-module-detect-earth-faults-on-these-inputs-signals/185/2 "2014-12-06T17:16:07Z")

</div>

A short between the +24VDC and earth will be detected. A short between the return line to the input channel will not be detected if no converter module is used:

For the input module SDI-1624, use input converter module BSDI-16UNI SM: digital input module type SDI-1624 placed in a redundant or non redundant IO Chassis FSC: digital input module type 10101/2/1 placed in a redundant or single IO rack