i need to know if the fire detector must connect to control panel directly or i can connect it to junction box first and then to control panel and what is the standard that illustrate this issue…

---

<div class="post-metadata">

**Author:** ![Sajid](https://forumautomation.com/user_avatar/forumautomation.com/sajid/32/3765_2.png) [@Sajid](https://forumautomation.com/u/Sajid)\
**Post date:** [November 30, 2014, 6:59am UTC](https://forumautomation.com/t/standard-for-fire-detector/179/2 "2014-11-30T06:59:19Z")

</div>

what kind of fire detector you want to connect IR type or thermal or Fusible loop ??

---

<div class="post-metadata">

**Author:** ![Hashem\_Ali\_Hashem](https://forumautomation.com/letter_avatar_proxy/v4/letter/h/958977/32.png) [@Hashem\_Ali\_Hashem](https://forumautomation.com/u/Hashem_Ali_Hashem)\
**Post date:** [November 30, 2014, 7:26am UTC](https://forumautomation.com/t/standard-for-fire-detector/179/3 "2014-11-30T07:26:17Z")

</div>

infrared type(IR)fire detector

---

<div class="post-metadata">

**Author:** ![instrumen](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/65b543/32.png) [@instrumen](https://forumautomation.com/u/instrumen)\
**Post date:** [December 1, 2014, 5:13pm UTC](https://forumautomation.com/t/standard-for-fire-detector/179/4 "2014-12-01T17:13:57Z")

</div>

Fire detectors are normally connecting in loop wise.From control panel single pair cable goes to all the detectors and get terminated at Control panel.There are restiction for maximum no: of detectors on single loop as per the manufacturer. Also, sometimes detectors are connected zone wise which means a single loop to dedicated for a particular zone

---

<div class="post-metadata">

**Author:** ![Hashem\_Ali\_Hashem](https://forumautomation.com/letter_avatar_proxy/v4/letter/h/958977/32.png) [@Hashem\_Ali\_Hashem](https://forumautomation.com/u/Hashem_Ali_Hashem)\
**Post date:** [December 1, 2014, 7:52pm UTC](https://forumautomation.com/t/standard-for-fire-detector/179/5 "2014-12-01T19:52:13Z")

</div>

i don’t mean the smoke detectors type ir but i mean flame detector such as FL3112 general monitors

---

<div class="post-metadata">

**Author:** ![fadhil](https://forumautomation.com/letter_avatar_proxy/v4/letter/f/b19c9b/32.png) [@fadhil](https://forumautomation.com/u/fadhil)\
**Post date:** [March 15, 2015, 5:15pm UTC](https://forumautomation.com/t/standard-for-fire-detector/179/6 "2015-03-15T17:15:48Z")

</div>

Need not necessarily be the case. The case discussed above is that of an addressable fire and gas system. Where as for PLC based safety systems you can connect them to JB’s and then lay a cable to the control room. If you have many detectors are wiring up individual detectors to the control room, you will be laying up lot of cables throughout your facility.