# Solution for PCDI(Peer Control Data Interface) and SCADA(Supervisory control and Data Acquisition address assignment?

**URL:** <https://forumautomation.com/t/solution-for-pcdi-peer-control-data-interface-and-scada-supervisory-control-and-data-acquisition-address-assignment/274>\
**Category:** Honeywell\
**Created:** [February 26, 2015, 8:30am UTC](https://forumautomation.com/t/solution-for-pcdi-peer-control-data-interface-and-scada-supervisory-control-and-data-acquisition-address-assignment/274 "2015-02-26T08:30:44Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![omega](https://forumautomation.com/letter_avatar_proxy/v4/letter/o/a6a055/32.png) [@omega](https://forumautomation.com/u/omega)\
**Post date:** [February 26, 2015, 8:30am UTC](https://forumautomation.com/t/solution-for-pcdi-peer-control-data-interface-and-scada-supervisory-control-and-data-acquisition-address-assignment/274/1 "2015-02-26T08:30:45Z")

</div>

If we gave both PCDI & SCADA address to any one tag and loaded to controller. After loading if u delete that address in particular tag and assign same address to same tag or different tags it wont allow.Pls suggest a solution?

---

<div class="post-metadata">

**Author:** ![instrumen](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/65b543/32.png) [@instrumen](https://forumautomation.com/u/instrumen)\
**Post date:** [February 26, 2015, 8:31am UTC](https://forumautomation.com/t/solution-for-pcdi-peer-control-data-interface-and-scada-supervisory-control-and-data-acquisition-address-assignment/274/2 "2015-02-26T08:31:42Z")

</div>

Hi omega,

For using same address use following steps Step1–\>Initially unassign PCDI & SCADA address and load to controller Step2–\>Now assign same address to same tag or other tags This problem will come when “Online Modification” of controller properties is checked.