# Smoke control in HVAC system for more number of floors

**URL:** <https://forumautomation.com/t/smoke-control-in-hvac-system-for-more-number-of-floors/4076>\
**Category:** Industrial Automation\
**Created:** [July 11, 2018, 2:12pm UTC](https://forumautomation.com/t/smoke-control-in-hvac-system-for-more-number-of-floors/4076 "2018-07-11T14:12:23Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![sivaranjith](https://forumautomation.com/letter_avatar_proxy/v4/letter/s/ba9def/32.png) [@sivaranjith](https://forumautomation.com/u/sivaranjith)\
**Post date:** [July 11, 2018, 2:12pm UTC](https://forumautomation.com/t/smoke-control-in-hvac-system-for-more-number-of-floors/4076/1 "2018-07-11T14:12:23Z")

</div>

An HVAC system can be implemented to serve on many floors. The normal HVAC system that serves all the floors of a building is shown below. For this building, the stairwells are pressurized in the event of a fire. The distribution ducts on each floor are shown in the picture.

 ![hvac%20fn](https://cdn.forumautomation.com/original/2X/7/71d9d99d0313d1d1d1d1d73b898130a599d50957.jpg)

## Smoke control by pressurization and exhaust:

 ![hvac%20f](https://cdn.forumautomation.com/original/2X/e/ee0afdf9f9fe89374e7544af27846bd502c05a6d.png)

In the event of fire in the system:

- The smoke damper in the return duct is open on the fire floor
- The rest of the smoke damper in the return duct are closed
- The smoke damper in the supply duct on the floor directly above and below the fire floor are open
- The rest of the smoke dampers in the supply duct are closed.

These damper settings are intended to:

- Concentrate exhaust on the fire floor
- Concentrate pressurization on the floor above and below the fire floor
- Prevent smoke from migrating to other zones through the return duct.

For this zoned smoke control system, the mode of operation of penthouse is explained in: [**click here**](https://automationforum.co/smoke-control-for-hvac-system/)

## Smoke control by exhaust only:

 ![hvac%20f2](https://cdn.forumautomation.com/original/2X/c/cbe9c717df337bb16aa2a0800db038e4e5f2dbe3.jpg)

The zoned smoke control consisting of the fire floor exhaust and exhaust of floor directly above and below the fire floor. In the event of fire in the system:

- The smoke damper in the return duct are open on the floor and floor directly above and below the fire floor.
- The rest of the smoke damper in the return duct is closed.
- All smoke damper in supply duct are closed.