# Problems related to positioner

**URL:** <https://forumautomation.com/t/problems-related-to-positioner/8813>\
**Category:** Field Instrumentation\
**Created:** [November 12, 2020, 5:01am UTC](https://forumautomation.com/t/problems-related-to-positioner/8813 "2020-11-12T05:01:37Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [November 12, 2020, 5:01am UTC](https://forumautomation.com/t/problems-related-to-positioner/8813/1 "2020-11-12T05:01:37Z")

</div>

**i have an control valve with SRD991(FF type) make positioner… normally on close loop, valve open at 50% positioner Air fail valve goes to Fail safe position. But while at Air return back valve move above 50% then slowly it comes to 50%… how to rectify this problem…? any suggestion or what action to be take on Positioner**

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [November 12, 2020, 6:40am UTC](https://forumautomation.com/t/problems-related-to-positioner/8813/2 "2020-11-12T06:40:51Z")

</div>

Try to bypass the positioner, Check the valve travel? If OK, then install back the positioner. Check the feedback arm, then calibrate it again.

Check the valve action on fail-safe. Visual check the stopper on top of diaphragm casing. If stopper provided how much percent check whether its split range. If FF check, the interlock, and sequence for the split.|

---

<div class="post-metadata">

**Author:** ![ZAINHUS](https://forumautomation.com/letter_avatar_proxy/v4/letter/z/eada6e/32.png) [@ZAINHUS](https://forumautomation.com/u/ZAINHUS)\
**Post date:** [November 16, 2020, 4:02pm UTC](https://forumautomation.com/t/problems-related-to-positioner/8813/3 "2020-11-16T16:02:58Z")

</div>

Dear Sir, Firstly you should determine what kind of actuator you use, pneumatic, motorized or hydraulic. Secondly to determine the reason of problem, do the following steps. 1- check the movement of valve and make sure it moving without any other unwanted forces. 2- secondly check the feedback (about 2 month ago I faced similar problem, it was the corrosion in teeth of feedback arm that change the variable resistance for deciding the position). 3- check the other controlling device. 4- check if there are a mechanical problems such as leakage in air. 5- also make sure the position controller has calibrated in the correct way ( the calibration method depends on your system and the manufacturing manual )

For any helps, I will be so happy to help you