# Problems related to gas detector

**URL:** <https://forumautomation.com/t/problems-related-to-gas-detector/9643>\
**Category:** Fire and gas\
**Created:** [July 24, 2021, 3:47am UTC](https://forumautomation.com/t/problems-related-to-gas-detector/9643 "2021-07-24T03:47:56Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [July 24, 2021, 3:47am UTC](https://forumautomation.com/t/problems-related-to-gas-detector/9643/1 "2021-07-24T03:47:56Z")

</div>

![image](https://cdn.forumautomation.com/original/2X/a/a2325240f2ed9314c84267b2824b09068d26b09f.jpeg)

GAS TOXIC DETECTORS

While calibration the zero calibration is ok, but the span calibration is faulty, if you look at the above display you can see a number. I have changed the PCB, sensor and also the cartridge but it is still faulty

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [July 24, 2021, 3:50am UTC](https://forumautomation.com/t/problems-related-to-gas-detector/9643/2 "2021-07-24T03:50:51Z")

</div>

Every gas detector will have the same issue when you don’t give sufficient pressure as how much it requires during calibration for span calibration.

There may have more chance of toxic cylinder low pressure or going to empty.

Or check the loop integrity well and try to reset from ICS panorma were ever accessible for soft key (accept/reset )inhibition as well as F&G panel hard key accept reset. Then go for calibration