# Problems related to flow transmitter

**URL:** <https://forumautomation.com/t/problems-related-to-flow-transmitter/8871>\
**Category:** Field Instrumentation\
**Created:** [November 27, 2020, 3:53am UTC](https://forumautomation.com/t/problems-related-to-flow-transmitter/8871 "2020-11-27T03:53:03Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [November 27, 2020, 3:53am UTC](https://forumautomation.com/t/problems-related-to-flow-transmitter/8871/1 "2020-11-27T03:53:03Z")

</div>

Magnetic FT totaliser measure 50ltr of solution passed but actual solution was 42 ltr and it was matched with solution tank LT. So how I resolved this problem.Why FT measures max flow than actual…? Solution = Hydrogen peroxide

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [November 27, 2020, 4:11am UTC](https://forumautomation.com/t/problems-related-to-flow-transmitter/8871/2 "2020-11-27T04:11:10Z")

</div>

1. Remove it from the line, power up, and check the zero. It should be stable, if not then set zero as per the procedure given for the particular model/ brand

2. After verifying zero, make sure fluid parameters are properly entered and verify the K factor for your application. This calculation should be given in the manual.

3. For a magnetic flow meter you need laminar flow and the line must at-least half full

4. power supply and signal cables must be properly grounded to their own potentials. Mag flow meter is very sensitive for grounding.