# Problems in TT valve due to temperature variation

**URL:** <https://forumautomation.com/t/problems-in-tt-valve-due-to-temperature-variation/8908>\
**Category:** Field Instrumentation\
**Created:** [December 5, 2020, 5:49am UTC](https://forumautomation.com/t/problems-in-tt-valve-due-to-temperature-variation/8908 "2020-12-05T05:49:25Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [December 5, 2020, 5:49am UTC](https://forumautomation.com/t/problems-in-tt-valve-due-to-temperature-variation/8908/1 "2020-12-05T05:49:25Z")

</div>

**If the line temperature falls by 20- 30 degree C due to some reason, the TT values start fluctuating drastically. Once power to the TT is recycled, its readings goes to normal. Please explain.**

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [December 5, 2020, 6:05am UTC](https://forumautomation.com/t/problems-in-tt-valve-due-to-temperature-variation/8908/2 "2020-12-05T06:05:02Z")

</div>

Check the body earth connection and earth leakage. Also, shield wire in the field side should be isolated( panel/jb side only connected). Also, check the damping time, the TT can be checked by RTD simulator.