**Power Factor (PF) = Real Power (kW) ÷ Apparent Power (kVA)**

For a sinusoidal AC system, **PF = cos φ** , where φ is the phase angle between voltage and current.

A lower power factor requires higher current to deliver the same kW load at the same voltage, increasing equipment loading and I²R losses. FORMULA:

Power Factor (PF) = kW ÷ kVA

Where: • kW = Real Power • kVA = Apparent Power • PF = Power Factor

EXAMPLE:

 ![1](https://cdn.forumautomation.com/original/2X/c/cf4645b1e55f75e8f3750fafd97dea9ef9af4c2b.jpeg)

Real Power = 800 kW Apparent Power = 1000 kVA

PF = 800 ÷ 1000 = 0.80

RESULT: Power Factor = 0.80

Another relation:

PF = cos φ

where φ is the phase angle between voltage and current.

KEY POINT: A lower power factor generally means higher current for the same kW load, which can affect cable, transformer, and switchgear loading.

Lower PF means **higher current for the same real power (kW)** at a given voltage. This can increase loading and losses in cables, transformers, and switchgear.

For modern systems with harmonics, **true power factor** can also include the effect of waveform distortion, so PF is not always simply equal to cos φ.