## Parallel Operation of Three Phase Transformers

**Parallel operation of [three-phase transformers](https://forumelectrical.com/tertiary-winding-in-transformers/)** means connecting two or more transformers to the same electrical busbar so they can **share the load simultaneously** and supply power together to a common system.

## Why Do We Use Parallel Operation?

1. **Increase Load Capacity** – Multiple transformers can share high loads when one transformer is not enough.
2. **Improved Reliability** – If one transformer fails, the other transformer can continue supplying power.
3. **Maintenance Flexibility** – One transformer can be taken out for maintenance without interrupting supply.
4. **Better Efficiency** – During low demand, one transformer can be switched OFF to reduce no-load losses.
5. **Future Expansion** – Additional transformers can be added as power demand increases.

## Conditions Required for Parallel Operation

For successful parallel operation, the following conditions must be satisfied:

## 1. Same Voltage Ratio

Both transformers must have the **same primary and secondary voltage ratings**. If the ratio differs, circulating current may flow between transformers.

## 2. Same Polarity

Transformers must have the **same polarity** ; otherwise, severe short-circuit currents may occur.

## 3. Same Phase Sequence

The **[phase sequence](https://forumelectrical.com/phase-sequence-indicator-calibration-procedure/) (R-Y-B)** of both transformers must match correctly.

## 4. Same Vector Group

The transformers should have the **same vector group** (e.g., **Dyn11 with Dyn11** ). Different phase displacement causes improper synchronization.

## 5. Same Percentage Impedance (%Z)

The **impedance percentage should be equal or nearly equal** to ensure proper load sharing.

## 6. Similar KVA Rating

Transformers should have **similar [kVA ratings](https://forumelectrical.com/how-to-calculate-the-kva-size-of-a-single-phase-three-phase-transformer/)** for balanced load distribution.

 ![2](https://cdn.forumautomation.com/original/2X/9/9bdeede4600479156e0750eca1605411b9be4619.jpeg)

## Example

Suppose two transformers are connected in parallel:

- Transformer 1 = **1000 kVA**
- Transformer 2 = **500 kVA**

The load sharing depends on impedance. If impedance is equal, the load is shared according to transformer capacity:

- **1000 kVA transformer → 66.7% load**
- **500 kVA transformer → 33.3% load**

## Advantages

Improved system reliability Increased power capacity Easy maintenance without shutdown Better operational flexibility Reduced downtime

## Disadvantages

Improper load sharing if impedance differs Circulating currents due to voltage mismatch Risk of overheating if one transformer becomes overloaded