# ON/OFF control action - Principle

**URL:** <https://forumautomation.com/t/on-off-control-action-principle/419>\
**Category:** Field Instrumentation\
**Created:** [May 10, 2015, 5:41am UTC](https://forumautomation.com/t/on-off-control-action-principle/419 "2015-05-10T05:41:25Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![automate](https://forumautomation.com/letter_avatar_proxy/v4/letter/a/51bf81/32.png) [@automate](https://forumautomation.com/u/automate)\
**Post date:** [May 10, 2015, 5:41am UTC](https://forumautomation.com/t/on-off-control-action-principle/419/1 "2015-05-10T05:41:26Z")

</div>

The ON/OFF control (two-position ) controller operates only when the measurement crosses the set point. In on/off control ,a valve would have only two positions fully opened or fully closed .As a result the output measurement always cycles above and below the set point.

Application of On/Off control

ON-OFF control is best applied to a large capacitance process that has essentially no dead time . Eg : large tank or bath

A system where dead time is short and rate of rise is slow can be handled adequately by ON/OFF control

---

<div class="post-metadata">

**Author:** ![carl\_e](https://forumautomation.com/letter_avatar_proxy/v4/letter/c/94ad74/32.png) [@carl\_e](https://forumautomation.com/u/carl_e)\
**Post date:** [August 4, 2016, 2:14am UTC](https://forumautomation.com/t/on-off-control-action-principle/419/2 "2016-08-04T02:14:04Z")

</div>

There is some hysteresis or deadband between the make/break or set/reset or on/off values.

Alarm relays trip exactly at setpoint, plus or minus the hysteresis.

On-Off control might do that or it might split the hysteresis half above the setpoint and half below the setpoint, like this

 ![](https://cdn.forumautomation.com/original/1X/4bf1b6573d30f247ed22ec05ae69a7181eb10be9.jpg)