# No Control Builder target in Configuration Studio

**URL:** <https://forumautomation.com/t/no-control-builder-target-in-configuration-studio/395>\
**Category:** Honeywell\
**Created:** [April 13, 2015, 6:45am UTC](https://forumautomation.com/t/no-control-builder-target-in-configuration-studio/395 "2015-04-13T06:45:35Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumen](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/65b543/32.png) [@instrumen](https://forumautomation.com/u/instrumen)\
**Post date:** [April 13, 2015, 6:45am UTC](https://forumautomation.com/t/no-control-builder-target-in-configuration-studio/395/1 "2015-04-13T06:45:36Z")

</div>

The installation was done as a SCADA install, rather than a Process install. When choosing the node type, the C200/300, ACE, SIM check box was unchecked.

The installation type can be confirmed via the 2 following registry entries. SCADA installation, Flex. [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“SCADA Client” [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”=“No”

Process installation, Flex. [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“Process Client” [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”="Yes”

SCADA installation, Server. [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“SCADA Server” [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”=“No”

Process installation, Server. [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“Process Server” [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”="Yes”

SCADA installation, Console Station. [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“SCADA Station” [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”=“No”

Process installation, Console Station. [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey"=“Process Station” [HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo\Engineering Tools\ “IsCDA”="Yes”

Note: The “[HKEY\_LOCAL\_MACHINE\SOFTWARE\Honeywell\TPS50\InstallInfo"InstallProductKey” may vary between releases.