# New flow factor if a DP transmitter is re-ranged from 25 kPa to 50 kPa

**URL:** <https://forumautomation.com/t/new-flow-factor-if-a-dp-transmitter-is-re-ranged-from-25-kpa-to-50-kpa/78>\
**Category:** Field Instrumentation\
**Created:** [October 2, 2014, 6:11pm UTC](https://forumautomation.com/t/new-flow-factor-if-a-dp-transmitter-is-re-ranged-from-25-kpa-to-50-kpa/78 "2014-10-02T18:11:04Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumen](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/65b543/32.png) [@instrumen](https://forumautomation.com/u/instrumen)\
**Post date:** [October 2, 2014, 6:11pm UTC](https://forumautomation.com/t/new-flow-factor-if-a-dp-transmitter-is-re-ranged-from-25-kpa-to-50-kpa/78/1 "2014-10-02T18:11:05Z")

</div>

A simple calculation is as follows: Q1/Q2 = Sq root of DP1/ Sq root of DP2 Q1 = Q2 \* Sq root of DP1/ Sq root of DP2

Q1 = New flow factor, Q2 =Existing flow factor DP1 = Transmitter new range, DP2= Transmitter existing range

```
	Q1 = Q2*SQ ROOT OF 50/25
	Q1 = 1.41*Q2

```

The new flow factor will be 1.41 times higher than the existing flow factor.