# Motor Megger Testing Procedure

## Objective

To check the health of motor insulation between:

**Phase to Phase**

**Phase to Earth (Body)**

**Winding to winding (for higher voltage motors)**

## Test Equipment Required

**Insulation Resistance Tester (Megger),**

**Digital Multimeter,**

**Discharge rod (for HV motors),**

**PPE (gloves, safety shoes, goggles) &**

**Lockout-Tagout (LOTO) kit.**

 ![image](https://cdn.forumautomation.com/original/2X/3/34f26581298ca793ec33592a0eda059f892590cb.jpeg)

## Safety Precautions

Isolate motor supply completely.

Apply **[LOTO (Lockout Tagout).](https://forumelectrical.com/loto-colour-coding/)**

Confirm no voltage using multimeter.

Discharge winding before and after testing &

Never touch terminals during test.

## Recommended Megger Voltage Selection

| **Motor Rated Voltage** | **Megger Test Voltage** |
| --- | --- |
| Up to 250 V | 250 V DC |
| 250 - 500 V | 500 V DC |
| 500 - 1000 V | 1000 V DC |
| Above 1 kV | 2500 V / 5000 V DC |

# Motor Megger Testing Procedure (Step-by-Step Procedure)

## Step-1: Isolate Motor

Switch OFF breaker.

Remove cable connections if possible.

Ensure motor is not connected to VFD (disconnect VFD output).

## Step-2: Clean Terminals

Remove dust, moisture, oil, or carbon deposits from terminal box.

## Step-3: Phase-to-Earth Test

Connect:

- Megger Line (L) → U phase
- Megger Earth (E) → Motor body
- Press TEST for 60 seconds

Note reading

Repeat for V and W phases.

## Step-4: Phase-to-Phase Test

Test between:

U – V

V – W

W – U

## Step-5: Record Readings

**Measure at:**

15 sec

30 sec

60 sec (standard value)

**Optional advanced tests:**

Polarization Index (PI Test) &

Dielectric Absorption Ratio (DAR)

## Insulation Resistance Values

**Rule of Thumb:**

Minimum IR (MΩ) = Rated Voltage (kV) + 1

| **Motor Voltage** | **Minimum Acceptable IR** |
| --- | --- |
| 415 V | ≥ 1.4 MΩ (preferably \>10 MΩ) |
| 6.6 kV | ≥ 7.6 MΩ |
| 11 kV | ≥ 12 MΩ |

**Healthy Motor Typically Shows:**

1). New motor: \>100 MΩ

2). Good motor: \>10 MΩ

3). Warning: \<5 MΩ

4). Dangerous: \<1 MΩ

> ### You can also follow us on [[color=#ff7700] **AutomationForum.co** [/color]](https://automationforum.co/), [url= [https://www.facebook.com/instrumentation.control](https://www.facebook.com/instrumentation.control)][color=#1E00A3] **Facebook** [/color][/url] and [url= [https://www.linkedin.com/showcase/81532759/feed/posts/](https://www.linkedin.com/showcase/81532759/feed/posts/)][color=#1E00A3] **Linkedin** [/color][/url] to receive daily Instrumentation updates.

> ### You can also follow us on [[color=#ff7700] **ForumElectrical.com** [/color]](https://forumelectrical.com/), [[color=#1E00A3] **Facebook** [/color]](https://www.facebook.com/profile.php?id=100091841583670) and [[color=#1E00A3] **Linkedin** [/color]](https://www.linkedin.com/showcase/91130242/feed/posts/) to receive daily Electrical updates.