# MCB - MCB is getting tripped during power up, how to solve this problem?

**URL:** <https://forumautomation.com/t/mcb-mcb-is-getting-tripped-during-power-up-how-to-solve-this-problem/8726>\
**Category:** Electrical\
**Tags:** switchgear\
**Created:** [October 26, 2020, 3:46pm UTC](https://forumautomation.com/t/mcb-mcb-is-getting-tripped-during-power-up-how-to-solve-this-problem/8726 "2020-10-26T15:46:20Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [October 26, 2020, 3:46pm UTC](https://forumautomation.com/t/mcb-mcb-is-getting-tripped-during-power-up-how-to-solve-this-problem/8726/1 "2020-10-26T15:46:20Z")

</div>

When I press the start or stop button in the MCB, and then when I power the MCB it is getting tripped, so what is the reason for that?

![image](https://cdn.forumautomation.com/original/2X/1/1d8eb21c4a57ec57399128e9b2bf707729324cef.jpeg)

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [October 26, 2020, 3:59pm UTC](https://forumautomation.com/t/mcb-mcb-is-getting-tripped-during-power-up-how-to-solve-this-problem/8726/2 "2020-10-26T15:59:23Z")

</div>

It could be because of two reasons

- At first we must check the power cable, so check its resistance and also check if the power cable is grounded
- Short circuit or overload could be the other reason

---

<div class="post-metadata">

**Author:** ![Rabert](https://forumautomation.com/user_avatar/forumautomation.com/rabert/32/6784_2.png) [@Rabert](https://forumautomation.com/u/Rabert)\
**Post date:** [June 19, 2025, 1:42pm UTC](https://forumautomation.com/t/mcb-mcb-is-getting-tripped-during-power-up-how-to-solve-this-problem/8726/3 "2025-06-19T13:42:20Z")

</div>

Because there is probably a short circuit (or) wiring issue in the control circuit (or) associated load, the MCB trips when you click the start/stop button and turn it on. It might also result from:

NO/NC connectors are not wired correctly.

Phase-to-phase or direct phase-to-neutral fault

Shorted motor (or) contactor coil

Overload condition

Check the load connections, insulation, and wiring.