# LSIG Protection in Circuit Breakers

**URL:** <https://forumautomation.com/t/lsig-protection-in-circuit-breakers/13898>\
**Category:** Electrical\
**Tags:** circuitbreaker\
**Created:** [February 19, 2026, 1:44pm UTC](https://forumautomation.com/t/lsig-protection-in-circuit-breakers/13898 "2026-02-19T13:44:45Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![Rabert](https://forumautomation.com/user_avatar/forumautomation.com/rabert/32/6784_2.png) [@Rabert](https://forumautomation.com/u/Rabert)\
**Post date:** [February 19, 2026, 1:44pm UTC](https://forumautomation.com/t/lsig-protection-in-circuit-breakers/13898/1 "2026-02-19T13:44:46Z")

</div>

LSIG protection is an advanced protection feature that is available in electronic trip units of Air Circuit Breakers (**[ACB](https://forumelectrical.com/troubleshooting-of-air-circuit-breakers-acb/)**) and high-end Molded Case Circuit Breakers (MCCB).

It provides four types of protection functions:

• L - Long Time Protection (Overload)

• S - Short Time **[Protection](https://forumelectrical.com/surge-protection-device-spd-working-principle-spd-types-functions-best-practices/)**

• I - Instantaneous Protection

• G - **[Ground Fault](https://forumelectrical.com/ground-fault-testing-procedure/)** Protection

These functions protect electrical systems from the

• Overloads,

• Short circuits and

• Earth faults with adjustable settings.

## 1). L – Long Time Protection (Overload Protection)

**Purpose**

Protects against the overload currents that occur when equipment draws more current than its rated capacity for a prolonged time.

**Typical Causes**

• Motor overload

• Excessive load on feeder

• Mechanical jam in motor

**Characteristics**

• Operates with inverse time delay

• Higher overload **→** faster tripping

• Lower overload **→** slower tripping

**Example**

• Breaker rating: 100 A

• Long time setting: 80 A

• Breaker trips if current exceeds 80 A for preset time.

**Adjustable Parameters**

• Long time pickup current (Ir)

• Long time delay (tr)

## 2). S - Short Time Protection (Short Circuit with Delay)

**Purpose**

Protects against the **[short circuits](https://forumelectrical.com/basic-short-circuit-current-calculation-methods/)** while allowing coordination with the downstream breakers.

**Why delay is required?**

Allows the downstream breaker to clear fault first and ensures the selective coordination

**Characteristics**

• Operates at high current levels (typically 2–10 x In)

• Includes intentional time delay

**Example**

• Short time pickup: 5 x In

• Delay: 0.3 seconds

• Breaker trips only if downstream breaker fails.

**Adjustable Parameters**

• Short time pickup (Isd)

• Short time delay (tsd)

• I²t ON/OFF option

## 3). I - Instantaneous Protection (Immediate Short Circuit Protection)

**Purpose**

It provides an immediate protection against the severe short circuits.

**Characteristics**

• No intentional delay

• Trips instantly when current exceeds preset value

• Typical Setting

8 -15 x In

**Example**

If In = 100 A

• Instantaneous setting = 1000 A

• Breaker trips immediately at 1000 A.

## 4). G - Ground Fault Protection (Earth Fault Protection)

**Purpose**

It protects against earth leakage faults

**Importance**

Prevents:

• Equipment damage

• Fire hazards

• Electrical shock

**Characteristics**

• Detects imbalance between phase and neutral currents

• Trips when leakage exceeds preset value

**Typical Settings**

• Pickup: 0.2 to 0.6 x In

• Delay: 0.1 to 0.5 seconds

## LSIG Protection Summary Table

| **Protection** | **Full Form** | **Protects Against** | **Time Delay** |
| --- | --- | --- | --- |
| L | Long Time | Overload | Yes (Inverse) |
| S | Short Time | Short circuit (with coordination) | Yes |
| I | Instantaneous | Severe short circuit | No |
| G | Ground Fault | Earth fault | Yes |

## LSIG Protection Curve

 ![image](https://cdn.forumautomation.com/original/2X/2/272870ffc14b7b48859f57d7f5287e999a470b6e.jpeg)

The protection curve has 4 regions:

1). Long time region → overload protection

2). Short time region → delayed short circuit protection

3). Instantaneous region → immediate trip

4). Ground fault region → earth fault protection

These curves ensure the proper coordination and protection hierarchy.

## Where LSIG Protection is used?

Common applications include:

• Air Circuit Breakers (ACB)

• High-end MCCB

• Main incomer breakers

• Generator protection

• Transformer protection

• Industrial panels

• Substations

## Example of LSIG Settings

Breaker rating: 1600 A

• L: 0.8 x In = 1280 A, delay 10 s

• S: 5 x In = 8000 A, delay 0.3 s

• I: 10 x In = 16000 A

• G: 0.4 x In = 640 A, delay 0.2 s

## Advantages of LSIG Protection

• Provides complete protection.

• Adjustable settings.

• Improves system coordination.

• Prevents nuisance tripping.

• Protects equipment and personnel.

## Difference Between LSIG and Thermalmagnetic Protection

| **Features** | **LSIG Protection** | **Thermal-Magnetic Protection** |
| --- | --- | --- |
| Accuracy | High | Moderate |
| Adjustable | Yes | Limited |
| Ground fault protection | Yes | No |
| Coordination | Excellent | Limited |
| Used in | ACB, advanced MCCB | Basic MCCB |

LSIG protection is an advanced and also an essential protection system used in modern circuit breakers.

It provides complete protection against overload, short circuit & ground faults while ensuring the proper coordination and safety of electrical systems.

> ### You can also follow us on [[color=#ff7700] **AutomationForum.co** [/color]](https://automationforum.co/), [url= [https://www.facebook.com/instrumentation.control](https://www.facebook.com/instrumentation.control)][color=#1E00A3] **Facebook** [/color][/url] and [url= [https://www.linkedin.com/showcase/81532759/feed/posts/](https://www.linkedin.com/showcase/81532759/feed/posts/)][color=#1E00A3] **Linkedin** [/color][/url] to receive daily Instrumentation updates.

> ### You can also follow us on [[color=#ff7700] **ForumElectrical.com** [/color]](https://forumelectrical.com/), [[color=#1E00A3] **Facebook** [/color]](https://www.facebook.com/profile.php?id=100091841583670) and [[color=#1E00A3] **Linkedin** [/color]](https://www.linkedin.com/showcase/91130242/feed/posts/) to receive daily Electrical updates.