# Is it possible to use ProfiBus communication cable along with 415v cable tray

**URL:** <https://forumautomation.com/t/is-it-possible-to-use-profibus-communication-cable-along-with-415v-cable-tray/9715>\
**Category:** Field Instrumentation\
**Created:** [August 10, 2021, 4:59am UTC](https://forumautomation.com/t/is-it-possible-to-use-profibus-communication-cable-along-with-415v-cable-tray/9715 "2021-08-10T04:59:43Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![instrumentationtechi](https://forumautomation.com/letter_avatar_proxy/v4/letter/i/50afbb/32.png) [@instrumentationtechi](https://forumautomation.com/u/instrumentationtechi)\
**Post date:** [August 10, 2021, 4:59am UTC](https://forumautomation.com/t/is-it-possible-to-use-profibus-communication-cable-along-with-415v-cable-tray/9715/1 "2021-08-10T04:59:43Z")

</div>

Can we lay ProfiBus communication cable along with 415v cable tray

---

<div class="post-metadata">

**Author:** ![ashlin](https://forumautomation.com/user_avatar/forumautomation.com/ashlin/32/3775_2.png) [@ashlin](https://forumautomation.com/u/ashlin)\
**Post date:** [August 10, 2021, 5:03am UTC](https://forumautomation.com/t/is-it-possible-to-use-profibus-communication-cable-along-with-415v-cable-tray/9715/2 "2021-08-10T05:03:34Z")

</div>

No, because the magnetic field from the 415v cables will interfere with the Profibus signal thereby corrupting the signal on the Profibus cable. you can do it if the 3 phase of 415 volts is balanced. Electrical power in the cable will generate magnetism and balanced 3 phases of 415 volts will cancel each other. Preferably data cable should be completely separate from the power line. Big current drawing conductor